Victron Multiplus II 12V - Model Comparisons

Поділитися
Вставка
  • Опубліковано 23 бер 2023
  • Logan explores the differences and updates in the new Victron Multi-plus II models, specifically the 12V options.
    The MultiPlus-II 2 x120V is the perfect one-box mobile solution for standard North American 50A 120/240VAC split-phase applications. Whether it is supplied from shore power or a generator, the MultiPlus-II 2x120V can accept and passthrough both lines of a 120/240V supply, with the capability to utilize the full 50A for charging and AC loads. When connecting to a single phase 120V supply, the L1 input of the MultiPlus-II 2x120V will accept incoming power for charging and passthrough, while combining the L1 and L2 outputs for single-phase 120V on each line.
    The MultiPlus switches to inverter operation when no AC source is available. The inverter output is also 120V single phase. In inverter mode, the MultiPlus-II 2x120V internally connects both lines L1 and L2 together to provide 120VAC to loads on either output. Therefore, in all connection circumstances, both sides of a distribution panel will be supplied with 120V. However, 240VAC is only available when the MultiPlus is supplied by a split phase 120/240VAC source. This prevents heavy loads such as water heaters or 240V air conditioners from discharging the battery.
    The MultiPlus-II 2x 120V has all of the expected features of our versatile inverter/charger range, including PowerControl, PowerAssist, Input Current Limit, two AC outputs, as well as parallel and 3ph configuration for larger capacity VE.Bus systems. Suitable for LiFePO4 batteries and a variety of other battery technologies.
    Features and Specifications:
    Multifunctional, with intelligent power management
    Two AC Outputs
    Virtually unlimited power thanks to parallel operation
    Split phase options
    On-site system configuring, monitoring and control
    Remote configuring and monitoring
    Input voltage range: 9.5 to 17 Volts DC
    Output voltage: 120 Volts AC +/- 2% @ 60 Hz
    Continuous output power (77° F): 3,000 Volt-Amps (VA)
    Zero load power: 19 Watts; 4 Watts in Search mode
    Maximum battery charge current: 120 Amps
    Dimensions: 22.75" x 10.82" x 5.8" inches
    Weight: 48.5 pounds
    5 year warranty
    Questions? For the fastest response please call 1.800.383.0195 or chat live on our website
    We are NAZ Solar Electric, formerly known as Northern Arizona Wind and Sun (NAWS). We have updated our name and our look to reflect who we are in 2023.
    What hasn't changed: Our ownership, our team, or our commitment to our customers.
    NAZ Solar Electric, or NAZ, is a supplier and distributor of solar equipment based in Flagstaff, Arizona. For over 40 years, we’ve designed systems and provided technical support for residential and commercial customers across the U.S.
    Phone: 800-383-0195
    Email: sales@solar-electric.com
    Website: solar-electric.com
    Use the online load calculator to estimate your average energy usage: www.solar-electric.com/solar/...
    NAZ Solar Electric would love to send you a price quotation on individual components or an estimate for a complete plug-and-play system. Let us know what you're looking for and we'll send you a quote within 24 hours (Monday - Friday).
  • Наука та технологія

КОМЕНТАРІ • 35

  • @NAZSolarElectric
    @NAZSolarElectric  Рік тому

    For a quicker response, please give our solar engineers a call (800) 383-0195 or send an email: sales@solar-electric.com. Thank you!

  • @robbehr8806
    @robbehr8806 Рік тому +3

    I bought a 12V MultiPlus II from Logan as part of a system. Logan and all of his co-workers are polite, professional, and helpful.

  • @matthewknight5641
    @matthewknight5641 10 місяців тому +2

    I love my victron 150-70 charge controller and im buying another 150-70 for another 1850 watt array very soon. Victron is expensive but seems to just work

    • @NAZSolarElectric
      @NAZSolarElectric  10 місяців тому

      It is very popular and we tend to agree! Thank you for the feedback!

  • @SublimeTree
    @SublimeTree Рік тому +1

    Thanks for the info. I'm configuring a system and I like the sounds of the multiplus 2 2x120v. But I don't no if it's best for a 24v system on a rv with a 30 amp system currently. Any thoughts would appreciated.

    • @MrSummitville
      @MrSummitville 11 місяців тому

      @WoudstraSublime - The MultiPlus 2X120 was specifically designed for 50 Amp 240v RV's.

  • @keithbar19741974
    @keithbar19741974 Рік тому +2

    Excellent video, what is not clear to me is the benefits of the original Multiplus over the new Multiplus II. In what use case would the original be the right choice? Usually when a new model of something comes out the old one is no longer produced but I still see lots of installers using the old version. I can see that for replacement you might want to get an old one but for a new install I can not see why you would not always go with the Multiplus II or IIx2

    • @NAZSolarElectric
      @NAZSolarElectric  Рік тому

      Yes, that is interesting!

    • @MrSummitville
      @MrSummitville 11 місяців тому +6

      @keithbar19741974 - The newer units MP-II ... The noise is much louder and the transformer hum is terrible. Consumers who installed the MP-II in an RV and even in a home are complaining about the noise.

    • @evergreeninvest
      @evergreeninvest 3 місяці тому

      Hi, for me if the original version was much cheaper and If I had the space than I would probably consider buying it. I'm researching my options to install a charger/inverter in my class C motorhome where I have space limitations.

  • @MrMinnesota99
    @MrMinnesota99 Рік тому

    Is the charger power factor corrected? What is the power factor while charging?

    • @robbehr8806
      @robbehr8806 Рік тому

      The Victron is manufactured in Europe, where rating in volt-amps is popular. For the 3000 VA version, I use a power factor of .8, which means 80% of the 3000 VA for converting to watts. So, the converted rating is 2,400 watts, which calculates to 20 amps at 120 VAC. BTW, most people try not to load any circuit for continuous use beyond 80% of maximum rating of the lowest rated component. Victron is really good, but a continuous load of 16 amps would be my maximum. I'd allow startup surges beyond that, but I limit running load to 16 amps.

  • @earlzeis35
    @earlzeis35 Рік тому

    More information on the add on current clamp please.

    • @NAZSolarElectric
      @NAZSolarElectric  Рік тому +1

      Earl, we would love to answer any additional questions you might have. You can chat with our engineers live on our website, call 1.800.383.0195 or if you leave a specific question here we will make sure it gets answered as quickly as possible.

  • @Noah-qt3rq
    @Noah-qt3rq Місяць тому

    I would also mention that the multiplus 2 has a lower idle consumption.

  • @igorkvachun3572
    @igorkvachun3572 Рік тому

    Yes solar system ☀⚡🔌🔋💡👍

  • @carlosreyes6448
    @carlosreyes6448 10 місяців тому +1

    Is power assist available on, all muti plus ii, inverters? Meaning 12v 24v and 48v.

    • @NAZSolarElectric
      @NAZSolarElectric  10 місяців тому

      Hi @carlosreyes6448 , yes it is! It's a feature of all Victron Inverter/Chargers Multi's and Quattro's.

    • @carlosreyes6448
      @carlosreyes6448 10 місяців тому

      @@NAZSolarElectric thank you, I appreciate it. And one more question. Is it 50amps. Input on 120v. And on the 2x120 50a for each leg? So 240v input on the 2x120v

  • @calculatedrisk114
    @calculatedrisk114 Рік тому +1

    I assume the multi plus 2 2x120 is a 3k watt total unit. Not 3k watt per leg?

    • @NAZSolarElectric
      @NAZSolarElectric  Рік тому +1

      From our engineering team: The Multi-II 2x120 is rated for an AC throughput of 50A (each leg). So the AC transfer is rated for 6kW per leg (typical of a common 50A RV Service) or 12kW total (at 240V). The inverter can invert and supply power (off-grid) up to 2.4kW (or 3kVA dependent on power factor). Several inverters can be added in parallel to increase the off-grid output proportionally. When the inverter is supplied with a 120V input, it will parallel L1/L2 and it can (in assist mode) boost the power output to both shared legs by up to +2.4kW (total). When provided a 240V input the inverter will split the legs (maintaining the split phase configuration) and in this mode the inverter will only support (assist) L1 with up to 2.4KW of boost power. For more information please feel free to reach out. Chat live on our website or call 1.800.383.0195

  • @awesomedee5421
    @awesomedee5421 Рік тому +1

    I want to see the 48V comparison

    • @NAZSolarElectric
      @NAZSolarElectric  Рік тому

      We do have more videos planned, however if you would like more info on the 48V please feel free out to our team. They are available via live chat on our website during business hours www.solar-electric.com or you can call 1.800.383.0195. Thanks for watching!

  • @jarvisbarthelmy6307
    @jarvisbarthelmy6307 11 місяців тому

    Do you have 24v to 220v 3000w units

    • @NAZSolarElectric
      @NAZSolarElectric  11 місяців тому

      These are not as common here in the US but we can get you any inverter Victron offers. We typically stock the 120V version but most of the 230V versions are available with minimal lead time. Feel free to call our team so we can get you a quote. 1.800.383.0195

  • @ronbridegroom8428
    @ronbridegroom8428 Рік тому

    I find the Victron series of inverter/chargers to be very confusing and not really suited for the North American home market due to an apparent lack of support for split-phase 240v

    • @john0270
      @john0270 Рік тому

      You need two units to run split phase 120/ 240.

    • @NAZSolarElectric
      @NAZSolarElectric  Рік тому +1

      From our engineering team: Victron inverters can be configured for native split phase output. We do this quite often and it involves stacking two inverters in a 180° offset orientation. One inverter would handle L1 and the other handles L2. It's a feature in the advanced configuration and it's possible with all Mufti and Quattro models. Victron products offer nearly unlimited configurability and there's really no other product on the market that compares. However, I do have to agree that some of these features can be very confusing. Luckily our team is here to help and support our clients with these advanced projects. We can even help by doing the configuration for you remotely, if needed.

    • @MrMinnesota99
      @MrMinnesota99 Рік тому +1

      I agree, why don't they just install the transformer from their autotransformer into these multiplus units?

    • @MrSummitville
      @MrSummitville 11 місяців тому +1

      @@MrMinnesota99 You could. But their main market is Europe. Europe does not have 240v/120v Split Phase, like the USA. So, they sell one unit and allow the USA Dealer or consumer the option to add the Autotransfomer and/or stack two units in Split Phase mode.

  • @sundancer442
    @sundancer442 3 місяці тому +1

    The original model looks like it would cool better. Any thoughts on this, anyone ? Cheers, Simon.

    • @NAZSolarElectric
      @NAZSolarElectric  3 місяці тому

      Hey Simon! We haven't noticed any measurable difference in cooling. It may depend on the setup and location though.