INSTALLING A DAIKIN R32 DUCTED AIR CONDITIONER AND WHY I USE 'MyPlace' from ADVANTAGE AIR.

Поділитися
Вставка
  • Опубліковано 3 жов 2024
  • HVAC⎜HVACR⎜REFRIGERATION⎜AIR CONDITIONING VIDEOS
    In this video I use 'MyPlace' by Advantage Air and explain my reasons for doing it.
    Below I have listed the Tool Bag and Tools that you see me use personally in my videos. By using these links it doesn’t cost you anymore however by doing so you are helping the channel grow.
    Thanks for the support!
    MILWAUKEE BACKPACK (I use this backpack as my Service Bag).
    www.amazon.com...
    FLUKE HVAC MULTIMETER KIT
    www.amazon.com...
    KLEIN (MEGGER) CONTINUITY INSULATION TESTER
    (This isn’t the megger I use personally because the one I use is old and isn’t available anymore. I recommend this one because its similar and does the same thing).
    www.amazon.com...
    VESSEL ELECTRIC SCREWDRIVER
    www.amazon.com...
    KLEIN CABLE STRIPPERS
    www.amazon.com...
    FIXINGS I USE FOR CONDENSING UNIT BRACKETS
    www.amazon.com...
    KNIPEX INSULATED LONG NOSE PLIERS
    www.amazon.com...
    KNIPEX INSULATED SIDE CUTTERS
    www.amazon.com...
    KNIPEX INSULATED SCREW DRIVERS
    www.amazon.com...
    PENCIL
    www.amazon.com...
    RATCHETING RIGHT ANGLE SCREW DRIVER
    www.amazon.com...

КОМЕНТАРІ • 49

  • @Gilzo_9
    @Gilzo_9 11 місяців тому +1

    Airtouch 5s are the goat rn for this. Should install one and see how you feel about it.

    • @maracservices
      @maracservices  11 місяців тому

      Everyone seems to be team air touch so I think you might be right. I should install one and see what I think! Cheers mate

  • @jbairinc.147
    @jbairinc.147 24 дні тому +1

    Condenser a bit tight to the building, not gonna breathe

    • @maracservices
      @maracservices  24 дні тому +1

      @@jbairinc.147fair enough. I just did more then what Daikin specifies in the Installation manual but I’ll take your advice

  • @mazayamazayanadira6862
    @mazayamazayanadira6862 11 місяців тому +1

    Good job mate😊

  • @ashrickard721
    @ashrickard721 Місяць тому

    I have temperature control sensor error and have no idea where the sensor is, I found 2 of them but they weren’t in use , no idea where the main one is

  • @Dynamacrtm
    @Dynamacrtm Місяць тому

    It sounds like the airhub can only cycle on/off based on the return air sensor and this can't be changed, is this correct? That's quite a limitation. Also the airhub can only set zones to +-2c of master. I assume myair doesn't have this limitation? Thanks.

  • @AGeurts
    @AGeurts 11 місяців тому +3

    Is there a reason why you choose Advantage Air over Airtouch? Price/Preferrence? Everytime ive dealt with an Advantage Air Control System its always had issues with there controls. Also You spoke about running the RJ45 Caballing next to power cable causing interference which is correct, But ive also heard you should not coil the cable over each other like that as it will also cause interference.

    • @maracservices
      @maracservices  11 місяців тому +1

      Hey mate, to be honest I genuinely don’t know much about Air Touch. When I first started using Advantage Air, Air Touch didn’t exist. I used air touch once a long time ago and didn’t like it but that’s not a fair comparison because it was a long time ago. Advantage air have had a shit load of issues over the last 10 years however that’s only with the e zone range. The MyAir range has been solid for me personally. I have used the MyGarage and MyView section on a couple of jobs too so maybe thats why I use advantage air. To be honest I think I need to try an Air Touch before I make any comments. I’m thinking about doing a comparison video.

    • @maracservices
      @maracservices  11 місяців тому +1

      Also, I didn’t know that coiling the cat 6 cable can cause interference. Good to know.

    • @AGeurts
      @AGeurts 11 місяців тому +1

      @@maracservices Yeh I had a training day at Actron last year & they explained that it obviously looks nice and neat when you zip tie it & Roll it up, but there is a chance youll have interference issues. A good investment would to be to purchase a RJ45 Crimper and start cutting back the lengths you dont need & crimp a new plug onto it.

    • @maracservices
      @maracservices  11 місяців тому

      @@AGeurts very interesting. Thanks for the tip. I actually have the crimper and make my own ends when roughing in jobs. I have the RJ45 bits in the car. In most cases though, I just use the roll they give you. From now on though I’ll just cut the end off. Cheers

  • @robalexander7348
    @robalexander7348 11 місяців тому +2

    A nice neat installation Mitch,Tom well done, that seems a rather a complicated system ! You are correct Good Surge protection is so critical these days, Plus a good earth... Mitch, you are a great A/C install tech,as i prefer wall mounting brackets also,as you can hose, sweep underneath to keep things tidy 😀 👍

  • @vanished001
    @vanished001 2 місяці тому

    The Advantage Air control can be converted to work with zigbee not wifi?

  • @bradgoodale3249
    @bradgoodale3249 27 днів тому

    Mitch do you guys have to put safety drain underneath the evaps in NSW.

    • @alkurdi4851
      @alkurdi4851 17 годин тому

      Yes you’re supposed to use the safety drip tray

  • @bevanmarr6589
    @bevanmarr6589 21 день тому

    Good install mate. What feet are you using for the outdoor unit?

    • @alkurdi4851
      @alkurdi4851 17 годин тому

      I think adjustable rubber feet , galavanised

  • @4snday
    @4snday 8 місяців тому +1

    Would you recommend Toshiba ducted air conditioner or Daikin only?

    • @maracservices
      @maracservices  8 місяців тому

      I’d personally go the Daikin mate

    • @4snday
      @4snday 8 місяців тому

      @@maracservices is there a reason why? I’m in the middle at the moment of getting quotes for either Daikin ducted or Toshiba. I was only going for Daikin, because everyone says Daikin. But I’ve had a few people say Toshiba because of its warranty, reliability and after sales support. I live in Sydney NSW, and my old one was a pioneer brand. Went strong for over 25 years. Now it’s a different ballgame with all these new brands and features.

    • @maracservices
      @maracservices  8 місяців тому +1

      @@4snday Yeah mate, it’s because Daikin and Mitsubishi Electric are manufactured in Thailand. Other brands like Fujitsu and Panasonic for example are manufactured in China. I personally despise anything made in China. I honestly couldn’t tell you where Toshiba are manufactured because I know so little about them. In my 17 years doing aircon, I hardly ever see Toshiba because they have such a low market share. They might be great, I wouldn’t know so do what feels best for you. Another thing to add, every single architect I’ve ever come across or any tender I’ve seen, has always made it a requirement to quote on Daikin or Mitsubishi electric. I don’t know why that is, but I’m assuming they feel the same way as me.

  • @J_D_Begins
    @J_D_Begins 11 місяців тому +2

    I installed a Daikin 14kw ducfed system today. 10 outlets 7 zones. Went with an air touch 5 system with sensors. Have had a fair few issues in the past with myair failing so have changed to air touch and so far its been really good. More options too.

    • @maracservices
      @maracservices  11 місяців тому

      I might have to give the air touch a go. Everyone seems to talk about it so they must be half decent. When you say more options, what exactly do you mean? I’m just curious. Cheers

    • @J_D_Begins
      @J_D_Begins 11 місяців тому

      @@maracservices there's more installer options and you have greater control and settings with an air touch. Also you can turn the zone on or off at the sensor which is handy.

    • @Dynamacrtm
      @Dynamacrtm Місяць тому

      Does air touch also allow you to specify a ITS as the master set point to cycle on/off the compressor? I want to have the baby room be the main driver of AC on/off and don't care much about the exact state of the rest of the house.

    • @J_D_Begins
      @J_D_Begins Місяць тому +1

      @Dynamacrtm yeah you can assign any zone as the master zone so the unit uses that set point to cycle off.

  • @finnnymarley761
    @finnnymarley761 10 місяців тому +1

    I’ve got the my air with a Daikin 16KW system.
    From what I’ve observed in cooling the system doesn’t actually ramp down even when temp has been met, it seems as though it runs at a min 2KWH
    It heating though it does. Is this right?

    • @maracservices
      @maracservices  10 місяців тому +1

      So when you say it doesn’t “ramp down”, I’m assuming you are talking about the air flow coming out of the vents?
      The outdoor unit where the compressor is located will definitely cycle off. To answer your question though, the indoor fan continues to cycle air even when the the system is at temp on cooling mode. This is normal. On heating however, when the system gets to temperature, the indoor fan will cycle off. The only reason it does this is because if it continued to cycle air whilst the outdoor unit was in the off state, you would get what would feel like a cold draft until the outdoor unit kicks back in. On cooling though you’ll never notice this so they just keep the fan on all the time to cycle air.
      Sounds like your system is running fine mate. Out of curiosity though, do you have solar and is that where you got the 2KWH measurement from?

    • @finnnymarley761
      @finnnymarley761 10 місяців тому +1

      @@maracservices Oh okay that makes total sense. I do have solar, but I just use a Powerpal that shows the houses energy usage. So I’m kinda guessing but it sounds about right

    • @maracservices
      @maracservices  10 місяців тому

      @@finnnymarley761 ah ok fair enough. I was just curious that’s all. When the system is at temp, the only thing drawing current is the indoor fan which is a tiny DC fan motor so I assume it would be similar to a ceiling fan being run.

  • @anwarjabar
    @anwarjabar 6 місяців тому

    I’m in the market for new ducted system, I’m thinking either Panasonic, Mitsubishi, Fujitsu or LG ?

  • @davedonnelly8681
    @davedonnelly8681 5 місяців тому +1

    Nice install. Myair is a great system and reliable. I had a Panasonic aircon with Myair installed in 2020 and used it for 4 year with no issues. The only thing that annoyed me with Myair is the need for a constant zone. I moved to a new house this year and installed an actron advance. Offers similar functionality but allows for .5c tempreature adjustment and no need for constant zone. I wish the neo app was as reliable as the My air app.

    • @maracservices
      @maracservices  5 місяців тому

      Thanks mate. The MyAir system actually doesn’t require a constant zone. That’s just something the installer put in there as a safety incase the home owner try’s to close all zones. You can change this setting from the tablet. I never put a constant zone in personally. Cheers

    • @davedonnelly8681
      @davedonnelly8681 5 місяців тому

      @@maracservices thanks for your response. Nice to know your accurately sizing your ducted systems for your clients. I think mine was a little over sized so needed to be there. Wish you were in qld I’d get you to do my ac work in a heart beat.

  • @J.k313
    @J.k313 11 місяців тому +1

    What do you think of airtouch? I've never installed a Myplace control system but it seems identical to airtouch.
    I guess it comes down to installer recommendation and price

    • @maracservices
      @maracservices  11 місяців тому

      For me, I have only installed one and I didn’t like it but to be fair, that was a while ago so take what I say with a grain of salt. Maybe I should try installing one and do a comparison. There’s an idea!

    • @danielmullooly3368
      @danielmullooly3368 7 місяців тому

      Done heaps of air touch 5 its amazing but they dont cover your time for warranty and have a few issues now and then

  • @leftywhat
    @leftywhat 8 місяців тому

    From memory, that's NBN FTTC model, and the clicking is the unit overheating (happened to my nonna). I'm 50/50 if I should go with Panasonic/MyAir5 or Actron Advanced with Neo and maybe 2 zones (or more if cost is somewhat reasoanble). Any thoughts/recommendations? On one hand, I like the idea of the Panasonic Naneox, and I like the MyAir 5 box unit in the roof (the vent control thing), but I don't really like the look of the tablet (looks like it's from 2006). The Actron I like Australian made, vertical discharge of the outdoor unit and the fact all parts including controller are from the same company, but I'm unsure about the outdoor unit noise and if its any louder compared to the Panasonic or ME units etc? Or was that the older units? And I'm not sure if one system can do something the other cannot etc? Like rampdown of the indoor unit etc?

  • @jackcarr2763
    @jackcarr2763 10 місяців тому

    What was the name of the convertor to cat6 box

    • @maracservices
      @maracservices  10 місяців тому

      So I think you might be referring to the “transformer”. The little black box that plugs into the black control box?

  • @troyturner981
    @troyturner981 8 місяців тому

    How much roof cavity space do you need for this? Desperate for ducted at my place.

  • @mikehaliburton4562
    @mikehaliburton4562 2 місяці тому

    Hi, great video content 👌 Looking at doing a ducted heat pump for single story home with fresh air ventilation.
    Was thinking mitsubishi with a lossnay system attached.
    Is there a daikin system that will take a ventilation system also?.

    • @maracservices
      @maracservices  2 місяці тому

      Thanks mate. Yeah Daikin has the same thing which is called a heat reclaim ventilator. Both the Mitsubishi one and the Daikin one are designed for commercial applications. I have fresh air in my house and it’s basically just a filtered fresh air vent that taps into my return air plenum. So I have roughly 10% fresh air in my house. I can adjust it manually to have more or less fresh air.

  • @LC-qi5ff
    @LC-qi5ff 11 місяців тому +1

    Nice. Have you looked at ways to isolate rooms/zones with dampers or something

    • @maracservices
      @maracservices  11 місяців тому

      Yeah definitely mate. Each room is its own zone that can be opened or closed. The zone motor has the ability to open and close in 5% increments so you can even balance the airflow from the controller.

    • @charliehannaford1348
      @charliehannaford1348 11 місяців тому +1

      Hey Mitch! Love your channel and your work. Is a drip tray only required if the indoor isn’t suspended?
      Cheers.

    • @maracservices
      @maracservices  11 місяців тому +1

      @@charliehannaford1348 hey, thanks so much! In regards to the drip tray, that’s honestly personal preference. There’s no rules for it, it’s just what ever the installer wants to do.
      For me, I’ve personally never had a problem with the units leaking so I don’t use drip trays. Daikin is fan forced and the drain pipe size is quite big so those two things mean it doesn’t ever get blocked in my opinion. Also unlike other brands, Daikins drip tray inside the unit is styrofoam so it’ll never rust out. In conclusion, I don’t use drip trays because I don’t have a way of getting them in the roof without cutting things. However if you have the ability to add a drip tray, that means you have gone the extra mile and that’s respectable. Cheers