Ductless Mini Splits: How to Prevent Leaks
Ductless Mini Splits: How to Prevent Leaks. Enjoy a quick video where we explain the simple yet important ways to ensure you don’t have leaks after installing your mini split.
Content:
00:00 Intro
00:38 Ductless Mini Split Condensate Management
01:26 Must Know about Condensate
02:42 Condensate Management Materials
03:40 Connecting Condensate Line
10:42 How to Exiting Condensate
#ductlessminisplits #ductless #GotDuctless
For more information please visit our store: www.gotductless.com
Переглядів: 517

Відео

Cielo Breez Max Mini Split Wifi Controller Review: Top 3 Reasons to Buy.
Переглядів 1,4 тис.2 місяці тому
Cielo Breez Max Mini Split Wifi Controller Review: Top 3 Reasons to Buy. Cielo Breez Max is a universal Wi-Fi controller with an in-room thermostat that gives you all the versatility you need to control and enjoy your mini split from anywhere in the world. Packed with features and backed with a 5-year warranty, Cielo is great tech for connecting to your mini split. Content: 00:00 Intro 00:41 Ci...
Mitsubishi vs. Fujitsu Mini Splits. In the Ring with Two Mini Split Giants
Переглядів 1,8 тис.2 місяці тому
Mitsubishi vs. Fujitsu Mini Splits. In the Ring with Two Mini Split Giants Content: 00:00 Intro 00:40 Brand Recognition 01:22 Support Networks 02:15 Contractor Networks 03:07 Product Warranty 04:18 Low Ambient Temperature Performance 05:38 Noise Level 07:14 Efficiency 08:07 Indoor Unit Styles 09:18 Product Offering 10:46 Single Zone vs. Multi-zone Compatibilities 12:54 Pricing 14:13 Durability ...
How to Choose a Mini-Split for a Converted Garage. Mitsubishi Ductless Single Zone Solution.
Переглядів 2,9 тис.2 місяці тому
How to Choose a Mini-Split for a Converted Garage. Mitsubishi Ductless Single Zone Solution. Content: 00:00 Intro 00:16 Mini-Split for a Converted Garage 01:00 What Mini-Split to Choose 01:23 Load Calculation for a Converted Garage 01:57 Mitsubishi 15,000BTU Single Zone System 03:01 Why the Mitsubishi FS Model? 05:18 Perfect for Airbnb Owners 06:14 Mitsubishi FS Outdoor Unit #minisplit #mitsubi...
Is MrCool a Good Brand or Not?
Переглядів 3,6 тис.6 місяців тому
Is MrCool a Good Brand or Not? Content: 00:00 Intro 00:18 Warranty Coverage 03:47 A Range of Products 04:04 Parts Availability & Customer Service 07:29 Conclusion #ductless #minisplit #mrcool Please visit our store at gotductless.com
Mitsubishi 18,000 BTU Hyper Heating Single Zone Mini Split Review
Переглядів 3,3 тис.6 місяців тому
Mitsubishi 18,000 BTU Hyper Heating Single Zone Mini Split Review Content: 00:00 Intro 00:17 MUZ-FS18NA with MSZ-FS18NA 00:29 Sleek Design of MSZ-FS18NA 00:44 Dual Vane Operation of MSZ-FS18NA 00:55 i-See Sensor of MSZ-FS18NA 01:12 Indirect or Direct Air Flow 01:21 Energy Saving Mode 01:26 Hyper Heating Technology of MUZ-FS18NA 01:59 Hard Start of MUZ-FS18NA 02:13 Quiet Operation 02:36 Warranty...
Top 6 Benefits of Mini Split Ductless Systems
Переглядів 1,6 тис.6 місяців тому
Top 6 Benefits of Mini Split Ductless Systems Content: 00:00 Intro 00:24 Top 6 Benefits of Mini Split 00:55 Benefit No 1 - Energy Efficiency 04:03 Benefit No 2 - Zoned Comfort 06:53 Benefit No 3 - Easy Installation 09:46 Benefit No 4 - Space-Saving Design 11:10 Benefit No 5 - Quiet Operation 12:37 Benefit No 6 - Improved Indoor Air Quality #minisplit #ductless #mitsubishi #mrcool #construction ...
Mitsubishi One-Way Ceiling Cassette Unit - Review
Переглядів 12 тис.6 місяців тому
Mitsubishi One-Way Ceiling Cassette Unit - Review Content: 00:00 Mitsubishi One-Way Ceiling Cassette Unit 00:29 Ceiling Installation Benefits 01:33 What is inside One-Way Ceiling Cassette Unit? 02:16 Access Panels 04:23 Best location of One-Way Ceiling Cassette Unit 06:12 How Loud is One-Way Ceiling Cassette Unit 07:07 Two Things to Consider 08:01 Condensate Management #minisplit #ductless #mit...
Mitsubishi vs. Mr. Cool: Which Mini Split Should I Choose?
Переглядів 44 тис.7 місяців тому
Mitsubishi vs. Mr. Cool: Which Mini Split Should I Choose? Content: 00:00 Intro 00:47 Mr. Cool DIY vs Mitsubishi 9K Single Zone System 02:34 Six Main Categories to Compare 03:22 Mitsubishi 9K GS Model Performance 07:11 Mr. Cool 9K Pro DIY Model Performance 09:59 Mitsubishi Features & Technology 11:27 Mr. Cool Features & Technology 12:59 Warranty & Longevity 13:49 Mitsubishi Features & Warranty ...
Pro Install: Mr. Cool Easy Pro DIY Step-by-Step Install with Pro Tips
Переглядів 16 тис.7 місяців тому
Watch a seasoned and experienced pro install a DIY Mr Cool Easy Pro Mini Split. This video will provide pro tips on how to install a mini-split so you avoid big mistakes. Receive step-by-step instructions to complete your installation efficiently and productively! Content: 01:04 Intro. Mr Cool Step-By-Step Pro Installation 05:17 Materials. Unpacking Mr Cool boxes 07:57 Required Tools for a Prop...
How to Deal with Mini Split Condensate? Condensate Management.
Переглядів 3,1 тис.9 місяців тому
How to Deal with Mini Split Condensate? Condensate Management. Content: 00:00 Intro 00:37 How to Deal with Mini-Split Condensate 00:45 Condensate Management 01:17 Wall Mounted Unit 04:35 Ceiling Cassette and Horizontal Ducted Units 05:31 Multi-Position Air Handler 08:56 How to Deal with Condensate #ductless #minisplit #Gotductless Please visit our store at gotductless.com/
Can a Mini Split Unit be Installed on an Interior Wall?
Переглядів 19 тис.10 місяців тому
Can a Mini Split Unit be Installed on an Interior Wall? Content: 00:00 Intro 00:40 Can a Mini Split Unit be Installed on an Interior Wall? 02:04 Line-Set Installation 03:35 Condensate Line Installation 06:10 Accessibility for Future Maintenance #minisplit #mitsubishi #gotductless Please visit us at gotductless.com
Mitsubishi Standard vs Hyper Heat Pump Systems. Which One is Right for You
Переглядів 28 тис.10 місяців тому
Mitsubishi Standard vs Hyper Heat Pump Systems. Which One is Right for You. Content: 00:00 Intro to Mitsubishi Standard vs Hyper Heat Pumps 00:33 What is Heat Pump 01:01 Inverter Technology 03:00 Hyper Heat Technology 04:14 Standard vs Hyper Heat 05:17 Performance, Heating Capacity 06:56 Sound Levels 07:54 Electrical Usage 08:22 Efficiency 10:18 Installation Complexity 11:26 Cost Comparison 12:...
Top Two Most Popular Mini-Split Brands in the USA. Mitsubishi vs LG Mini-Split Systems
Переглядів 34 тис.11 місяців тому
Top Two Most Popular Mini-Split Brands in the USA. Mitsubishi vs LG Mini-Split Systems. The best two mini-split brands in 2023. Content: 00:00 Intro 00:32 Mitsubishi Mini-split 00:43 I-See Sensor 01:24 Air Distribution 01:50 One-Way Cassette Unit 02:52 Quiet Operation 03:26 Filter Access 04:10 LG Mini-split 04:17 Picture-Frame Wall Unit 05:54 WiFi Capability 06:41 Art-Cool Mirror Wall Unit 07:3...
How to Size a Mini-Split System: Tips for Properly Sizing a Ductless Mini-Split System
Переглядів 37 тис.Рік тому
How to Size a Mini-Split System: Tips for Properly Sizing a Ductless Mini-Split System. Content: 00:00 Intoro 00:50 What is BTU 01:24 Main Factors for Sizing Mini-Spit 02:19 Room Dimensions 03:20 Windows & Doors 03:57 People 04:18 Insulation 04:51 Location 05:18 Other things to consider 06:14 Sizing a Single and Multi-zone 07:20 Sizing a mini-split system. Btu Calculator #mitsubishi #minisplit ...
Mitsubishi Electric MHK2 Wireless Thermostat Kit Overview
Переглядів 9 тис.Рік тому
Mitsubishi Electric MHK2 Wireless Thermostat Kit Overview
Mitsubishi Electric PAC-US445CN Thermostat Adapter Overview.
Переглядів 3,1 тис.Рік тому
Mitsubishi Electric PAC-US445CN Thermostat Adapter Overview.
Mitsubishi Electric Kumo Cloud Wireless Interface
Переглядів 5 тис.Рік тому
Mitsubishi Electric Kumo Cloud Wireless Interface
Mitsubishi Electric. Three Most Popular Mitsubishi Wireless and WiFi Controls Overview.
Переглядів 4,6 тис.Рік тому
Mitsubishi Electric. Three Most Popular Mitsubishi Wireless and WiFi Controls Overview.
Got Ductless: Customized Product Support. Happy Shopping with Got Ductless.
Переглядів 1,4 тис.Рік тому
Got Ductless: Customized Product Support. Happy Shopping with Got Ductless.
Welcome to Got Ductless - One Stop Shop for Ductless Mini Splits
Переглядів 928Рік тому
Welcome to Got Ductless - One Stop Shop for Ductless Mini Splits
Mitsubishi Kumo Cloud WiFi Controller vs. Airzone Aidoo ductless mini-split WiFi Controller
Переглядів 13 тис.Рік тому
Mitsubishi Kumo Cloud WiFi Controller vs. Airzone Aidoo ductless mini-split WiFi Controller
Line Set Covers for Ductless Mini Split Units. Line Set Cover Ideas and How to use it.
Переглядів 13 тис.Рік тому
Line Set Covers for Ductless Mini Split Units. Line Set Cover Ideas and How to use it.
Top 3 Most Common Mini Split Questions for Ductless Multi-Zone Systems
Переглядів 1,1 тис.Рік тому
Top 3 Most Common Mini Split Questions for Ductless Multi-Zone Systems
Most popular types of ductless mini split indoor unit types.
Переглядів 2,6 тис.Рік тому
Most popular types of ductless mini split indoor unit types.
How to Mount a Mini Split Outdoor Unit. Mounting Options for the Ductless Mini Split Outdoor Unit.
Переглядів 8 тис.Рік тому
How to Mount a Mini Split Outdoor Unit. Mounting Options for the Ductless Mini Split Outdoor Unit.
Are Mini Split Air Conditioners Worth It? Pros & Cons of Ductless Mini Splits.
Переглядів 25 тис.Рік тому
Are Mini Split Air Conditioners Worth It? Pros & Cons of Ductless Mini Splits.
Mitsubishi Mini-Split Wall-Mounted Indoor Units.
Переглядів 19 тис.Рік тому
Mitsubishi Mini-Split Wall-Mounted Indoor Units.
Cleaning supplies for ductless mini-splits units.
Переглядів 285Рік тому
Cleaning supplies for ductless mini-splits units.
What's An In-Store Ductless/Mini-Split Consultation? | Got Ductless
Переглядів 1,1 тис.5 років тому
What's An In-Store Ductless/Mini-Split Consultation? | Got Ductless

КОМЕНТАРІ

  • @ssnydess6787
    @ssnydess6787 33 хвилини тому

    Nice video. I would appreciate one going through the steps of install. There have been problems related to that install here at my housing development that I believe are related to connecticity. Thanks for explaining the component relationship of this 3 part system.

  • @heroesandzeros7802
    @heroesandzeros7802 2 години тому

    Mitsubishi vs. Mr. Cool? Neither. Consider the EG4. It runs on solar panels or household 110VAC. Cools in summer, heats in winter, on solar panels. My electric bill loves it.

  • @michaelhauck2832
    @michaelhauck2832 15 годин тому

    Did a little reading in the manual and spoke with a couple more experienced techs- how involved is cleaning the blower wheel since, to my understanding, its resting in the "V" space above the evaporator coil

  • @hitechrr
    @hitechrr 3 дні тому

    Mr. Cool warranty. Limited Lifetime* & 7 Yr Replacement* on Compressor + 5 Yr Parts 4th Gen DIY®s have an optional LIMITED LIFETIME compressor warranty*, a 7-year compressor replacement* warranty, and a standard 5-year parts warranty for the original registered owner.

    • @gotductlessusa
      @gotductlessusa 22 години тому

      That is true. Thanks for the feedback!

  • @bobnomura2068
    @bobnomura2068 5 днів тому

    No contact, the Mitsubishi is the winner. For the DIY guy, if they want to do it every 3 years, on the Mr cool system, more power to them. I'd rather have a system that I don't worry about for 12 years. One person commented on the audio quality, I have to agree.

    • @gotductlessusa
      @gotductlessusa 22 години тому

      Thanks for the feedback! You are right. We put a lot of effort into the video and then found our audio to be trash :'(

  • @helihoot
    @helihoot 6 днів тому

    Hello, I have a Senville SENL24CD/IX. I am needing to remove the squirrel cage fan but there is no access to the motor retaining screw. Based on the maintenance manual it looks as though the evaporator needs to be lifted up on the motor side to access the retaining screw. Unfortunately the refrigerant lines going through the wall will not allow me to raise the evaporator. Is this the design? It's basically impossible to do unless I pull the unit off the wall way high in the air just for routine service?

    • @gotductlessusa
      @gotductlessusa 22 години тому

      No clue! We don't sell Senville due to issues like this :)

    • @helihoot
      @helihoot 20 годин тому

      @@gotductlessusa I did find a video that shows how. It's a bunch of hard to get to screws and you lift the right side of the evaporator just enough to get a screwdriver in there to loosen the retaining screw. Thank you for responding. I will be replacing this unit with a Mitsu since the cleaning didn't fix it.

  • @JussPerfect
    @JussPerfect 6 днів тому

    Just to feedback that your voice is super soft but the sudden music is loud.

    • @gotductlessusa
      @gotductlessusa 22 години тому

      Thank you for the feedback. We can always be better!

  • @davidcr131991
    @davidcr131991 7 днів тому

    Working for minisplit Brand innovair?

    • @gotductlessusa
      @gotductlessusa 22 години тому

      No, this is a Mitsubishi specific product.

  • @juliaveir8556
    @juliaveir8556 7 днів тому

    Does the position of the head unit relative to the outdoor unit affect the need for a pump? My understanding is that a head unit creates the condensate. We're getting varying quotes for a ductless mini split for a garden level basement. The head unit is on an exterior wall, about two feet above ground. So i assume gravity will take care of it. The line set coming out of the head unit, through the exterior wall, can be sloped. However, maybe the head unit being lower than the top of the outdoor unit somehow compromises that? I can't figure out why they are quoting for a pump. It's a well known, locally owned company. They just keep saying "you need it in a basement install"even after the site visit.

    • @gotductlessusa
      @gotductlessusa 22 години тому

      As long as the wall mounted unit is above ground level and is mounted on an exterior wall there should be no reason for a condensate pump. It does not matter if the indoor unit is below the outdoor unit as the condensate comes from the indoor unit and is not related to the outdoor unit. There might be another factor at play that you can ask about?

    • @juliaveir8556
      @juliaveir8556 21 годину тому

      @@gotductlessusa the other two companies did not feel we needed it. We are also in an extremely dry climate (front range of Colorado) so I can't believe there will be much condensate anyway. We have a Mitsubishi hyperheat unit heating and cooling a finished garage: the condensate coming off that is barely detectable. I just wanted an outside opinion that wasn't affected by price. Thanks so much

  • @aks20002
    @aks20002 9 днів тому

    I am considering at 4-zone mini split ( having 4 wall consoles ) to air condition 2 large ( 400 sq ft ) bedrooms and 2 small bedrooms ( 200 sq ft ) on the same floor. The LG offering - LG-L4H36F09091212 - has much better dialed down capacity as it can go down to 8400 BTU for cooling and 10080 for heating. A similar 4-zone system for Mitsubishi - MXZ-4C36NA4-U1 - dials down to 11700 for cooling and only 18300 for heating. This is very important difference as my two small bedrooms will have very light load particularly in shoulder season. But Mitsubishi has an advantage - they offer 6K btu indoor ceiling cassette and LG has lowest as 9K. Surprisingly, Mitsubishi has no min cooling/heating rating for the ceiling cassette, while LG does say that its 9K wall console has min cooling/heating as 4270/4600 btu - which makes it competitive if not better from 6K Mitsubishi ceiling cassette for small rooms. Do you think I should opt for LG option , despite Mitsu being perceived as higher quality product ?

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      If you set your remote controllers to Auto for Mitsubishi you would avoid this issue altogether. In our opinions and experience, we have seen less issues with Mitsubishi overall.

  • @sophiegrisom
    @sophiegrisom 10 днів тому

    Mr Cool is easiest to install, but much pricier than a Medea mini-split and vacuum pump ($70 Amazon). You need the pump to suck down the supply lines and indoor unit before opening the pre-charged refrigerant. Also allows you to cut-flare the tubing for correct length rather than having to coil extra tubing like w/ Mr Cool. You can use the vac pump later on your automotive AC. Medea (China) makes most mini-split brands (Pioneer, Della, ...) except a few (Mitsubishi, Daikin, ...). A few mini's (ex. EG4) can run on a combo of grid plus solar panels (direct, no inverter needed).

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      That is one way of doing it. Except good luck getting replacement parts for Midea units

  • @Jimmy-rd5ig
    @Jimmy-rd5ig 10 днів тому

    You didnt mention anything about humidity. If you live in a very humid area, it makes sense to slightly undersize the unit so that it runs longer and will dehumidy.

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      That is true! This is an issue if you completely oversize and the room gets chilled faster than it can dehumidify. This is especially a factor in more humid climates. thanks!

  • @matthewerikson4243
    @matthewerikson4243 11 днів тому

    Is a 2x6 wall deep enough to run a line inside? I’d like to run the inline set inside the wall for a few feet before I could get down into a space behind a kneewall and run the line set out the end of the house in a traditional way.

  • @mondavou9408
    @mondavou9408 12 днів тому

    A Btu was originally defined as the amount of heat required to raise the temperature of one pound of liquid water by one degree Fahrenheit at a constant pressure of one atmospheric unit. There are several different definitions of the Btu that differ slightly.

  • @ron521
    @ron521 14 днів тому

    How far can I run the line set. I know that the more corners the line set has to bend around the shorter the total distance. Does this distance depend on the compressor model. I have a mitshabishe hyper heat.

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      It depends on the model. Typically non-smart multi outdoor units have a max piping length of 82 ft per indoor, and 160-230 total piping length max.

  • @CowboyPants-h5p
    @CowboyPants-h5p 18 днів тому

    Will not subject myself to this horrid audio quality. Bye.

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      Fair enough. Tune into other videos where our audio is better

  • @troyabercrombie1969
    @troyabercrombie1969 19 днів тому

    I have a question looking and doing a mini split in my garage. My choices are bosh or mitsubishi?

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      Feel free to call into our main line 866-399-0206 and we can help you. Bosch private labels Chinese units while Mitsubishi manufacturers their own

  • @tomford5925
    @tomford5925 20 днів тому

    Great video! I just installed a new Fujitsu mini split. Going to dump the condensate next to Condenser outside but leave a little space between both drain lines so I can check both flex lines from time to time to make sure they're both draining. Mark you're a great presenter and your videos answer alot of my questions. thanks for the great content! please keep the videos coming!

    • @gotductlessusa
      @gotductlessusa 8 днів тому

      Happy to help! Thanks for staying tuned :)

  • @ChuckRichardson-o6i
    @ChuckRichardson-o6i 24 дні тому

    Can mini splits use Geothermal energy?

    • @gotductlessusa
      @gotductlessusa 3 години тому

      It is possible but requires some engineering

  • @quadcityracing
    @quadcityracing 24 дні тому

    Does the indoor fan run continuously on each of these units, or is there a fan cycle option?

    • @gotductlessusa
      @gotductlessusa 21 день тому

      There is a fan option that is standalone. The indoor fan does run continuously when it is heating and cooling. That is why the system is efficient. It doesn't turn off and on constantly. Ramping on the fan is what consumes energy.

  • @quadcityracing
    @quadcityracing 24 дні тому

    Great video, well stated.

  • @quadcityracing
    @quadcityracing 24 дні тому

    Thanks for the hyper heat specs. It would be cool to know how they acheive almost 90% heat when zero degrees. What’s the air temperature output at zero degrees?

    • @gotductlessusa
      @gotductlessusa 21 день тому

      It depends on whether the unit is trying to maximize its capacity. If you only have some indoor units working then indoor temperature won't change. If all of them are working then you would get a lower temperature in each room because your outdoor total capacity has dropped. The drop wouldn't be significant at 90% capacity.

  • @quadcityracing
    @quadcityracing 25 днів тому

    Dude audio stinks

  • @DelEast740
    @DelEast740 28 днів тому

    As an HVAC sole proprietor I charge way more labor per hour to install a mini split that I would a furnace or an air conditioner. At least $1,000 just for me to get into an attic

  • @Movie16Master
    @Movie16Master 28 днів тому

    I was reading through the manual of the hyperheat and saw it mention a gas line. Does it require gas for solid heating?

    • @gotductlessusa
      @gotductlessusa 21 день тому

      No gas lines required. It is strictly electric. The outdoor unit needs to be installed a distance away from gas lines.

    • @ludercrous
      @ludercrous 17 днів тому

      @@gotductlessusa ALL heat pumps (and AC only systems) absolutely need gas lines, but these are for transferring refrigerant gas and liquid between the outdoor and indoor units - NOT fuel gas lines (natural gas or propane for a furnace). I suspect @Movie16Master was confusing the two.

  • @DNTMEE
    @DNTMEE 29 днів тому

    It seems you just glossed over the fact that the Mr. Cool is 115V and the Mitsubishi is 230V. That's a *BIG* difference! That's also the main reason the the Mitsubishi has such better ratings. Pretty much all appliances run more efficiently when they are made to use 230V. Also many people who install one or the other don't have 230V at the location they want to put one in. I don't think you emphasized this difference at all. It also makes the other comparisons pretty much invalid, making this a REALLY _"apples to oranges"_ comparison.

    • @gotductlessusa
      @gotductlessusa 29 днів тому

      That is actually a good point. Thanks for the input. What we've seen is people buy Mr. Cool mainly because they save on labor and equipment cost while still having a 7 year warranty. Efficiency ratings and such are an added bonus. But nonetheless you have a valid point.

  • @xpkareem
    @xpkareem 29 днів тому

    please sort out your audio setup.

  • @DaveHaynie
    @DaveHaynie Місяць тому

    Excellent video. I'm currently having a garage built, and I'm trying to decide between through-the-wall and mini-split for cooling... and maybe the one or two days a year I might need heat, here in Florida. The main issue with mini-split seems to be cost, and a big part of that is cost of installation, so I'm starting to understand why Mr. Cool is a bit pricier than some -- it's got nearly everything you need in the kit and the pre-pressurized lines allow self-installation, at least if you're experienced at home improvement/repair. Thanks for making this, it's really helpful.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Mini splits are great because its not very intrusive to your build. You drill a 2.5" hole and that is all, while a PTAC through the wall would require you to find an exact match sized unit if you need to replace it in the future. Plus, mini splits are more efficient to run so your utility bill will be less. Thanks for watching

  • @CockyMike911
    @CockyMike911 Місяць тому

    If I have wi-fi adapters on all the heads and using the Kumo cloud app, will the system work if the internet service is down? It seems like that was the case the last time I used this system.

  • @chembrad
    @chembrad Місяць тому

    Effing false title. These are not made in the US.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Top 4 Brands in the US if you like that better. Those brands are manufacturers though

  • @UBGood
    @UBGood Місяць тому

    Could not continue to watch this video due to the sound issues 😮

    • @gotductlessusa
      @gotductlessusa Місяць тому

      That's our fault! Bottom line: go with Mitsubishi if you got $$$ and want to have a long lasting system. Go with Mr. Cool if you're on a budget and want a DIY project :)

  • @CristhianGallo-romero-zb3kq
    @CristhianGallo-romero-zb3kq Місяць тому

    Since this is a prepressured…. Are you not allowed to cut the copper lines down so there won’t be to rolled up?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      You cannot cut it shorter since it is pre-pressured. That is why we coiled it horizontally under the outdoor unit.

  • @KevinBurdine-k4t
    @KevinBurdine-k4t Місяць тому

    I am about ready to buy a mini split heat pump system. But don't know if I should get two 12K BTU units or a 12K and a 9K. Those I'm looking at are both Pioneer Diamonte series, so same features, same 19 SEER, etc. Either way should cover the 18,200 btus required to heat and cool my small home (that's based on only square footage… I may need at least 20,000 based on poor insulation and windows. The price difference of the two units (12k vs 9k) is only about $20 currently for the prices I'm looking at with Home Depot. (The 18K is $300 more than those and the 24K is out of the question for me.) Of course, I'd be happy to pay a little more to get the second 12k, ***** UNLESS THE 12K WILL COST SIGNIFICANTLY MORE TO RUN THAN A 9K.***** That is the important question that I need answered. A 12K would go in the larger Living Room/ Kitchen area; The small bedroom/bath area will get either a 12K or 9K. BTW: So far it looks more cost effective to get two units than to get one larger unit that feeds two blower heads. Plus with two separate units I'll always have a backup and I can shut one down in mild temps. Also one larger unit feeding two blowers will require longer lines which adds cost.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Running a 12k will not cost significantly more to run than a 9k. The real question is what does your space require. If you have poor insulation and poor window insulation then I would be conservative on sizing. The last thing you want is to spend thousands and it won't work properly or will be inefficient.

    • @KevinBurdine-k4t
      @KevinBurdine-k4t Місяць тому

      @@gotductlessusa Thank you so much! You say the 12K energy consumption will not be much more than a 9K. Is that true only for inverter+ variable speed compressors (because the bigger unit can slow down to operate like a 9K?) That is what I am interested in btw.

  • @tenspeedtears
    @tenspeedtears Місяць тому

    The Mr Cool leak detection is useless as you will not find a HVAC company to work on these units…

    • @gotductlessusa
      @gotductlessusa Місяць тому

      You can check the Mr. Cool website for contractors near your zip code. There will be contractors that don't want anything to do with it but that doesn't mean that is true across the board

  • @reinerzanotelli7358
    @reinerzanotelli7358 Місяць тому

    What's the difference between Mitsubishi Electric PAC-US445CN or Mitsubishi Electric PAC-US444CN?? Thanks

    • @gotductlessusa
      @gotductlessusa Місяць тому

      They are essentially the same module. The 445 works with all the new Mitsubishi equipment that they have added to their catalog. Mitsubishi is only making the 445s now.

    • @reinerzanotelli7358
      @reinerzanotelli7358 Місяць тому

      Thanks man! And we use Mitsubishi with tekmar thermostat, and always we have to use a relay for reverse valve OB, do you have another way to works no using relays? Thanks

  • @Shoeshoe1
    @Shoeshoe1 Місяць тому

    👍

  • @miltonsaucedo2223
    @miltonsaucedo2223 Місяць тому

    3 questions 😅 this cielo max will make any non-wifi enabled unit, essentially wifi-enabled correct? or does the unit itself have to be wifi-enabled to begin with? 2- can one cielo max be used to operate two different heads? or do you need one cielo for each head? 3- can you wire this to the electricity cables that run to a traditional thermostat and power it that way? thank you!

    • @gotductlessusa
      @gotductlessusa Місяць тому

      the unit itself doesn't really have a way of being wifi enabled. That's just a nice way of saying the unit doesn't come with built in wifi. Yes, you can use the Cielo to make any ductless unit wifi capable. You need 1 Cielo per indoor head. We are not sure. It is a good question to ask the manufacturer. The unit is meant to be plugged into a 115v outlet and wirelessly connect to an indoor unit.

    • @miltonsaucedo2223
      @miltonsaucedo2223 Місяць тому

      @@gotductlessusa thank you!

  • @gregdawson1909
    @gregdawson1909 Місяць тому

    The Mitsubishi is not aimed at diy, however in the small size single head units they are diy adjacent, the units come precharged you just have to evacuate the linesets, which is not that hard, and the equipment is pretty cheap. When you get into the multi zone units from them they get exponentially harder for a diy install with having to add freon to makeup for your linesets and your indoor air handlers, vs the mr cool, which seems like its pretty much diy no mater what. The other thing to note is that decibels are not a linear scale, every 3 DB is roughly twice the noise, so every plus 3 is significant.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Mitsubishi is not a DIY system. Mitsubishi likes their equipment to be installed by a professional so they know the refrigeration and electrical connections, and start-up, are done correctly. There are large portions of the installation that can be done by someone handy but the final connections should be done by a professional. On the other hand, Mr. Cool is a fully DIY product for those customers that might not be able to afford a trade contractor (can be very pricey). Mitsubishi is definitely quieter than Mr. Cool that's for sure.

  • @Willi-g9o
    @Willi-g9o Місяць тому

    If one goes with mini splits in a new build, does every room need one?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Not necessarily. It depends on zones. If you have an open space then you can do 1 large unit. Or if you have a master suite that has a bathroom and closet then you would just have 1 unit in the master bedroom and that would cover the bathroom and closet. Mitsubishi also has mixed options for multi-zones that allows you to use both ducted units and ductless units on the same outdoor. Let's say you wanted all the bedrooms to be the same temperature and the rest of the house to be ductless units. With Mitsubishi units you can do that. Mr. Cool you would need to be strategic with design as they don't have that hybrid mix option.

    • @Willi-g9o
      @Willi-g9o Місяць тому

      @@gotductlessusa thank you for your explanation

  • @ede4345
    @ede4345 Місяць тому

    I was thinking of buying the central 2.5 ton unit does anyone know how reliable these are ?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      They are technically a Gree manufactured private labeled product. Many other companies use the Gree system so they are wide spread. The warranty is very high on central ducted units, offering a 10 year parts, compressor, and labor warranty (covering labor up to the cost of the unit).

  • @michaelschroeder6256
    @michaelschroeder6256 Місяць тому

    Mitsubishi mini splits way too expensive for the amount of problems you’re going to have in the cost of getting those problems fixed

    • @gotductlessusa
      @gotductlessusa Місяць тому

      It definitely depends on whether the installation was done properly. If steps were skipped you will experience issues left and right

  • @edbuscus360
    @edbuscus360 Місяць тому

    I’m not sure where all this information is coming from, but I work with these systems almost daily. From my experience, Fujitsu is noticeably quieter than Mitsubishi, and their customer support is more responsive. However, one downside of Fujitsu is their ceiling-mounted units, which are more labor-intensive to install and have fewer features compared to Mitsubishi's ceiling mounts. Aside from that, Fujitsu is quieter all day long, their customer support is better, they are more cost-effective and efficient, and I have three supply houses fully stocked with parts and new units. I moved away from Mitsubishi during the hype when parts and units were nearly impossible to get for months. Now, I can visit my local Fujitsu dealer and get three heads and a condenser the same day. As for durability, the tests seem to favor Mitsubishi, but I haven't noticed any significant difference between the two when installing or running them over time. While I’ve seen more Mitsubishi units break down, there are also more of them out there, so it might be an unfair comparison. All in all I think Fujitsu is the way to go and that's coming from someone who has installed and serviced them both.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Thanks for the feedback. This information is coming from the manufacturers themselves, our employees' experiences, and our experiences of selling 1000s of units for both brands and having to deal with warranty on the backend. Yes, Mitsubishi has had stock issues but Fujitsu has suffered as well especially this summer with the looming refrigerant changes. All in all both are reputable companies and this video is meant to compare information and let people make their own conclusions

  • @broli720
    @broli720 Місяць тому

    I have a hyperheat system and kumo cloud. Installer for the second set of units i got did not install the thermostat. I'm wondering if I should just get the MK whatever thermostat that comes with the unit or just get this since it's cheaper?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      You can buy the MHK2 but the installation is more tedious and you'll pay more. The Cielo would be a cheaper option and easier installation. Plus it comes with wifi if the second set of units don't have kumo cloud.

    • @broli720
      @broli720 Місяць тому

      @@gotductlessusa Sorry i didn't clarify, all units have kumo cloud set up. Main objective is to have an in room thermostat for guests to tweak. I guess that's not necessary since i have the remote for all units plus Kumo cloud? Only other pro i can think of is the homekit integration. I don't use amazon or google

  • @DavidRynne-h8k
    @DavidRynne-h8k Місяць тому

    I’m looking at a new house and they have already roughed in the piping and wiring for an LG system. If I was to move to Mitsubishi would the wiring be the same and would the condensate line also line up.The units are on interior walls so changing things at this point would be challenging. Thanks in advance.

    • @michaelschroeder6256
      @michaelschroeder6256 Місяць тому

      I don’t know anything about the LG’s, but I can tell you this much about Mitsubishi’s the cost of a Mitsubishi and the install price was $9000 for a single head unit. I’ve had it for seven years and I’ve spent 6000 on repairs. And the unit has broke down again I am currently looking into a Blue Ridge or a Della system

    • @gotductlessusa
      @gotductlessusa Місяць тому

      The line-sets and wiring is 90% all the same. The pipe sizing might be different on 24k-36k indoor units. The smaller units 7k-18k are all the same. Wiring is all the same as well. The only variance might be on the high voltage line that runs to the outdoor depending on the outdoor unit you go with.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      @michaelschroeder6256 It sounds like the contractors in your area are overcharging you for labor, and potentially didn't install the unit correctly if you are experiencing such issues and paying that much for corrections. The system is under warranty for the first 6 years so you wouldn't be paying for parts. You do pay for labor of replacement parts but paying $6k for anything is crazy.

  • @jmcmob608
    @jmcmob608 Місяць тому

    Thank you very much...

  • @simplytruth9729
    @simplytruth9729 Місяць тому

    I would not try diy-unless you are gifted with various mechanical and electrical skills and you have a friend to help. Approximately $14000-17000 for 3 zones. Installed Samsung The ac is not the most attractive item hanging in the room, but I guess function over fashion. It looks more modern/industrial than my decor. I did not pay attention to size of box hanging in a 20x15’ room. I would have picked a smaller size if I had known. I am thankful for the relief though. Very thankful.

  • @speedwayman100
    @speedwayman100 Місяць тому

    if you have 2 1800 sq ft homes and you had a new ac unit put in one home and whatever minisplits that would be required for the other home and they ran the same amount of time and everything was equal would the minisplits save more on your electric bill?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      It would be more efficient with mini splits. Reason being most likely your amp draw will be less to begin with and the SEER ratings of mini split outdoors are higher than conventional ac on average

    • @speedwayman100
      @speedwayman100 Місяць тому

      @@gotductlessusa good to know,thank you!

  • @AlexanderHuzar
    @AlexanderHuzar Місяць тому

    I have the Breez Max, but you didn't talk at all about the product tiers. Specifically you didn't mention anything about the Cielo's ability to coordinate the rooms via multi-zone mini-split control and also you made no mention of the Comfy Max feature - both these things are why you'd purchase the Max over the lower price point products.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      Those are some good points. Thanks for pointing them out!

  • @ryanhuth-thehuthgroupatkel4385
    @ryanhuth-thehuthgroupatkel4385 Місяць тому

    I have a question. I had 5 units installed a few weeks ago and the unit in our bedroom is making some loud popping/cracking noises all night. We have to turn it off to sleep. We've been told that the unit experiences expansion and contraction and that is why it makes these loud noises. Apparently, Mitsubishi is aware of this and that there's nothing that can be done. Has anyone else had this problem?

    • @hardsole34
      @hardsole34 Місяць тому

      Experiencing the same popping/cracking noises issues. Especially during winter, not so much during summertime. Like you mentioned, heard it's "normal" expansion/contraction noise.

    • @gotductlessusa
      @gotductlessusa Місяць тому

      As far as what we know there is going to be expansion and contractions. Sometimes this is due to refrigerant distribution based on which indoor units are on vs, off. However, there is natural expansion and contraction that might result in noises due to copper rubbing up against the plastic casing. We have heard that noise levels can be lowered if you apply lubricant on the copper coil where it is close to rubbing against any plastic. This has helped other customers that have experienced this issue.

    • @tjinytjiny6615
      @tjinytjiny6615 20 днів тому

      I have 5 of these units installed. 4-9KS/1-18K. 4 installed about 5 years ago, I added a 9K unit. I have never had a noises of any kind from the units. My 18 did develop a leak which turned out to be a drain reservoir most likely cracked during the install. My installer sent a crew, they diagnosed the problem, ordered me a new unit, installed it no expense to me. Took about a week to do because they had to order an 18K unit, or it would’ve been done the first day. Noises of any kind are not normal, I’d insist the installer change out the unit especially if the noise wakes you. I also not use my system for cooling, I only used the heat the first week of the first winter I had it.

  • @phigo4kins
    @phigo4kins Місяць тому

    I Bought a 12K BTU 115V Unit that Came with One indoor Handler. Can I Add Another Indoor Unit To Cool/Heat Another Small Room? If So, How? Do I Have To Get The Same Make/Model Of Indoor Unit? Or Can I Get One From A Different Maker?

    • @gotductlessusa
      @gotductlessusa Місяць тому

      You cannot add another indoor unit to that outdoor unit. You would either have to upgrade the outdoor unit that you have or install a separate system. You have to use the same brand if you plan on upgrading your outdoor unit from a 1 zone to a 2 zone