  • @barnybrewman1571
    @barnybrewman1571 Рік тому +5

    I have used this 3000 watt inverter to power my off grid house for over 2 years now. It runs 24/7, and has performed flawlessly so far. My biggest load is a 2000 watt deep fryer and it will run that while the refrigerator, TV, small freezer, and a few lights are on. It's probably not built for continuous use, but it hasn't let me down yet. I recently bought a second one for a back-up.

    • @LDSreliance
      @LDSreliance  Рік тому

      Nice! Glad to hear it works well as a main source of power.

    • @rafaelmt1000
      @rafaelmt1000 Годину тому

      Does this work well for a 3/4 HP pool pump? you have to remember that they have a starting surge.

  • @marscruz
    @marscruz 4 роки тому +5

    Resistive loads like heaters are the easiest kind of load to put out. Inductive loads, like motors that are used in refrigerators and AC units, are the real test of an inverter like this. I would like to see the ability of the inverter to take a 2.5 or 3kW inductive load without tripping and I would like to see what its power factor looks like near full load. Also would like to see what the output voltage wave form (sine wave) looks like. You gave this inverter the easiest type of work to do. I realize you are not an electrician or engineer. I hope people will realize that just because you can run a heater off this inverter that it may not be suitable for inductive types of loads. Thanks.

    • @LDSreliance
      @LDSreliance  4 роки тому +1

      That is true. But as I stated in the video, I don't have the battery power to test that kind of surge.

  • @wandahelmer1038
    @wandahelmer1038 3 роки тому +3

    I own 2, 12 volt models, they start 1horse motors and my fridges and freezer I also run the reliable 24 volt model in 4000 watts, I find that the 4000 watt one does not run as well as the 12 volt 3000 watt models. I have pulled 2500 watts at 200 plus amps they (3000 watt model) did the pull with no hiccup. Yes I would recommend them. I have now run all three for over 3years, stand by power is less than a amp, I run them up to 6 to 8 hours a day in winter and 24hrs during summer. Off a 4600 watt solar grid.

    • @LDSreliance
      @LDSreliance  3 роки тому

      Good to hear! I am getting reports that these inverters do not have any short circuit protection. Any experience with that?

    • @wandahelmer1038
      @wandahelmer1038 3 роки тому

      @@LDSreliance I ground them properly and only run them in a off grid manner, I don't run them to their fullest power thats why I have 3 of them, I also have 2 600 watt and one 800 watt reliable pure sine wave, all of them have their own duty, and none of them are run to full power, I have a 500 watt pure sine wave reliable that is a little funky but works, it is also over 3yrs old, I never have short circuited them, don't plan on either, if I can help it. Like I said they do their job nicely, my electronics (stereos tvs radios chargers run ok) for the price I'm happy.

    • @LDSreliance
      @LDSreliance  3 роки тому +1

      Sounds good. Thanks for the info.

  • @PatricksDIY
    @PatricksDIY 3 роки тому +3

    0:17 The terminal cover is in the bag with the fuses that you show at this time, it pops on and states in the manual to put it on when in use. You must have overlooked it.

    • @LDSreliance
      @LDSreliance  3 роки тому +1

      Yes I did. I realized that after the video. I don't know what I was expecting it to look like but a tiny piece of clear plastic was not what I was expecting. I guess it works though.

  • @joelvillanueva784
    @joelvillanueva784 3 роки тому +3

    I have a 2000 watt 24 volt one. It works 💪perfectly 🥰💞👌😌🙌👏🥰

    • @LDSreliance
      @LDSreliance  3 роки тому

      Awesome. They seem like they are great. I'm a bit worried that they don't seem to have short circuit protection, though.

  • @matthewrichmond5179
    @matthewrichmond5179 3 роки тому +2

    New Comment on an older vid. How is it running a year later? Follow up vid or comment?
    Good looking systems can have crap components, yet still test good for unboxing. Great vid and good info!

    • @LDSreliance
      @LDSreliance  3 роки тому +2

      Still running well. The only issue that I have heard of and have not found myself or dared to duplicate for obvious reasons is that the terminal block may not be fused or protected. Again, that is only a rumor and I can't confirm or deny it. And I have no plans to test that. But it may be wise to take extra precaution around that.
      I am going to feature this inverter in some 12V lithium battery testing videos soon so if you are interested in that make sure you subscribe and keep an eye out. This inverter has the potential to push my Jericho batteries to their limit and I want to see what they can do.

  • @nvlvdave
    @nvlvdave Рік тому +1

    I'd like to see tests on items with high inrush current like a small welder or a motor. Nice job and great info!

    • @LDSreliance
      @LDSreliance  Рік тому +1

      Unforunately, I don't have anything like that and it can easily handle the air conditioners that I have tried it with. Thanks for watching!

    • @nvlvdave
      @nvlvdave Рік тому +1

      @@LDSreliance An A/C unit is a perfect example of a high startup current load. So it did well? Still using the inverter?

    • @LDSreliance
      @LDSreliance  Рік тому +1

      Yes, it did fine with a 10,000 BTU window unit. I still use it in my shed but I don't tax it very hard. I have some ac outlets hard wired to the ac output in addition to the built in ones on the front. I mostly use it for charging my lawn equipment batteries and smaller stuff.

  • @GabrielSBarbaraS
    @GabrielSBarbaraS 3 роки тому

    Hi LDSreliance , I have a cheap 3000 watt inverter and most always use it for 1500 watts only, ( 12.5 amps ) ; seems to work well with that type of use. Thanks for the video.

    • @LDSreliance
      @LDSreliance  3 роки тому

      That would definitely work well. You are welcome!

  • @mega-hb4re
    @mega-hb4re 11 місяців тому +2

    I had one and it work great for 3 years till I upgraded the newer version with better performance

    • @LDSreliance
      @LDSreliance  11 місяців тому +1

      Thats good to hear. I have used it on a few installs and in one of my own setups for years and it has worked well. I heard there was a ground issue with the AC output bar or something but never could confirm that.

    • @mega-hb4re
      @mega-hb4re 11 місяців тому +1

      Apparently some have ground issues but with the new model specially the 5000 watts is the same size as the 3000 and I’m able to use my 15k btu roof top air and a small 5000 btu in the back of my 30 footer with no issues. Is worth the buy , just sell the old one You won’t regret it

    • @LDSreliance
      @LDSreliance  11 місяців тому +1

      Nice, glad to hear.

    • @rafaelmt1000
      @rafaelmt1000 2 години тому

      Does this work well for a 3/4 HP pool pump? you have to remember that they have a starting surge.

    • @mega-hb4re
      @mega-hb4re Годину тому

      @@rafaelmt1000 if you get the new version which is black and 5000 watts with a surge of 10,000 shouldn't be a problem. Just remember to use the high output lines to connect heavy stuff, do not use the regular outlet . I use a 10 g wire extension cord cut the end and put it in the high output lines

  • @rafaelmt1000
    @rafaelmt1000 2 години тому

    Does this work well for a 3/4 HP pool pump? you have to remember that they have a starting surge.

    • @LDSreliance
      @LDSreliance  37 хвилин тому

      Maybe. 3/4 is possible. 1hp I would probably say no. It will also depend on the battery you have connected to it.

  • @mannyfragoza9652
    @mannyfragoza9652 3 роки тому +1

    i got the same Inverter i did the MOSFET upgrade (not sure what the benefits are since it still cant run my 6000 BTU old school AC) It runs my 5000 BTU AC with ease

    • @mannyfragoza9652
      @mannyfragoza9652 3 роки тому

      Now watching your video after a few mins now i know why i couldn't run my 6000 BTU AC. The reg. AC plugs cant supply enough of surge power. Ill have to hookup a junction box like you did to run the full power of the Inverter. Thanks LDS for this video it was very helpful

    • @LDSreliance
      @LDSreliance  3 роки тому +2

      You are welcome! Yeah the AC outlets cannot output the full power of the inverter. Hard wiring will do it for you. If you don't have a cable, you can use any 3 prong extension cable and cut off the male end and use those 3 leads to connect to the inverter and then the female end can be used to connect your AC.

    • @mannyfragoza9652
      @mannyfragoza9652 3 роки тому

      @@LDSreliance thats a great idea i might have an extension here i can use .

  • @bigbigrichie
    @bigbigrichie 4 роки тому +1

    They work great I have two 3000 watt running my house

    • @LDSreliance
      @LDSreliance  4 роки тому

      Nice. How long have you been using them?

    • @bigbigrichie
      @bigbigrichie 4 роки тому +1

      @@LDSreliance 2 years now..I'm gonna make a new video soon maybe sunday or monday

    • @LDSreliance
      @LDSreliance  4 роки тому

      Good to know. I plan to put mine into service soon.

    • @bigbigrichie
      @bigbigrichie 4 роки тому

      @@LDSreliance yea they have a soft start function to them so they won't start a compressor but everything else fine

    • @LDSreliance
      @LDSreliance  4 роки тому +1

      I was tempted to test my compressor. I guess they dodged a bullet because that would have been bad.

  • @SsDiBoi
    @SsDiBoi 3 роки тому +2

    Luv the connection hack cause the price of connectors r out of effin control

  • @gundog5
    @gundog5 4 роки тому +2

    I have 5 of these Reliable inverters, a 2,000W (1 year old), two 2,500W (2 years old), and two 3,000W (1 year old) all 24V, though. All are still working as expected.
    The 3,000W inverters are used at an off-grid recreational camp each on 2 separate solar power systems, plus a 2,500W inverter spare for redundancy. They power most everything at camp, including varying lights, small water pumps (a shower & a kitchen sink), power tool batteries, laptops, cellphones, two TV's, a coffee maker, fans, a cellphone booster, a small 500W window-shaker air-conditioner, a shop vacuum, and a microwave.
    Only things the 3,000W inverters don't like are the bigger things like the shop air compressor, pressure washer, and a 1,500W camper ceiling air-conditioner. Apparently, the surge is too much. Have to run the generator for these things.
    Agree the cables that come with the inverter are not sufficient long-term or for high loads, but can work for initial setup with lighter loads. I'm using 2/0 cables for my setup.
    All of my inverters came with a clear plastic cover that goes over the power block terminals. Check in the bag the fuses came in. It's probably in there.
    Overall, I've been very happy with all of them. They are a good value for what they are and have been working well for this type of application.
    The other 2 inverters I have are at home for backup power and various testing/ hobby projects.

    • @LDSreliance
      @LDSreliance  4 роки тому +2

      Great feedback, thanks! I will look for that plastic guard. I thought the bag was just fuses but maybe I am blind.

  • @jhonnyjoeel-bedewi2196
    @jhonnyjoeel-bedewi2196 3 роки тому

    Nice man, you are cool and frank :) yet good vid ha. Here it goes....2thumbs up for you ;) Stay safe bro.

    • @LDSreliance
      @LDSreliance  3 роки тому

      Thanks! I really appreciate that.

  • @jackpatteeuw9244
    @jackpatteeuw9244 4 роки тому +1

    From other reviews ... The standard outlets SHARE the same internal power wires, so COMBINED you should not exceed 1800W !!

    • @LDSreliance
      @LDSreliance  4 роки тому +1

      Yes, more accurately it is 15A combined for the 2 outlets. You cannot get the full 25A output unless you use the terminal block and hard wire in your circuit.

  • @bingosunnoon9341
    @bingosunnoon9341 2 роки тому +1

    Did you look at the sine wave with an oscilloscpe? That's what interests me the most.

    • @LDSreliance
      @LDSreliance  2 роки тому

      No, I do not have an o-scope. I wish I did!

    • @bingosunnoon9341
      @bingosunnoon9341 2 роки тому

      @@LDSreliance Maybe you could get one of those pocket sized scopes on ebay. They are OK for showing wave forms like this. They are only 25 dollars. That will make your channel stand out.

    • @LDSreliance
      @LDSreliance  2 роки тому

      I'll look into it. Thanks!

  • @larryjanson4011
    @larryjanson4011 2 роки тому

    whats with the cheap "add on" wire block?. is that factory? if it is, that alone is a deal killer as it looks cheap. and might have "problems" including safety issues.

  • @yoshiyukisekiguchi8957
    @yoshiyukisekiguchi8957 Рік тому

    Hi...I am still trying to figure out which size of inverter do I need for 1200 watt air blower for my car cleaning purpose ...I got dryer but not yet decide which lithium battery and also inverter ...
    Do you thing this example work? 12v 100 amp per hour battery and pure sine 1500watt inverter combination ...simple math I thought was 12.8 x100watt....= 1280 watt can cover this dryer???
    However what I doubted was continue use as more than 5 minutes or more...
    What I am not so familiar was peak out put wattage kinds staff.
    Will you give me some advise. It will be greatly appreciated...I am sort of very tight budget on this.
    But if I can use longer time I think I can make some investment.

    • @LDSreliance
      @LDSreliance  Рік тому +1

      The battery will be the limiting factor for your scenario. If you go with a 12V battery you would have to make sure the battery could handle the constant current output for a 1200W load. Your basic math is correct... 1200W / 12V = 100A. So the battery would have to be able to provide 100A constantly to run that load. However, that is the limit for most 100Ah lithium batteries on the market right now. And I would not run one at its limits. I would find one with a 150A constant output to make sure it can go over 100A, which the air blower may end up doing after you factor in other variables.

    • @yoshiyukisekiguchi8957
      @yoshiyukisekiguchi8957 Рік тому

      @@LDSreliance thanks a lot...that was exactly I though ...I will look for battery that has more than 100ah...125 140 150 ah...it was great help. Thx again.

    • @LDSreliance
      @LDSreliance  Рік тому +1

      Good luck! Wish I still had some of my Jericho batteries in stock. They would easily do the trick.

    • @yoshiyukisekiguchi8957
      @yoshiyukisekiguchi8957 Рік тому

      @@LDSreliance thx again, I just order battery charger first because some limited deal from amazon ..20 A universal charger ...this is for me very slow project no rush...when money is available...I buy one by one.

    • @LDSreliance
      @LDSreliance  Рік тому

      I am the same way. I don't buy things on credit so usually that means I have to take things slowly as I have spare cash.

  • @Espinal_424
    @Espinal_424 2 роки тому

    I do mobile detailing. Would this run a small vacuum and pressure washer plugged at the same time?

    • @LDSreliance
      @LDSreliance  2 роки тому

      Those are both pretty serious loads. There are too many variables to say for certain, not the least of which are the power requirements of the two devices, but I would say one at a time you will be good but both at the same time is iffy and possibly dangerous.

  • @lennylhchen
    @lennylhchen Рік тому

    Smoke come out after 5 months of norma use. Turns out the connection wire were too thin and burnt.
    No good.

  • @harrrytoool1391
    @harrrytoool1391 3 роки тому +1

    Not recommended. Other you tube reviews show zero short circuit protection. Risk of fire or damage to unit is possible and therefore expense.

    • @LDSreliance
      @LDSreliance  3 роки тому +1

      That is definitely not a good thing, but also not a surprise. I know David Poz really likes these.
      Even if I know an inverter has good protection I am still going to use a breaker or fuse on its input to protect from fire. It may still destroy the inverter but I'm not super worried about a fire.

  • @bodiddley82
    @bodiddley82 4 роки тому +1

    I need help. I have 2500w. Wired into service truck. Turned it on an red light lit an alarm buzzes.

    • @SsDiBoi
      @SsDiBoi 3 роки тому

      U might wanna find another connection

    • @SsDiBoi
      @SsDiBoi 3 роки тому

      A cops tool 4 problem solving huh

    • @SsDiBoi
      @SsDiBoi 3 роки тому

      Dont 4get the hellcat puncher chic cop

  • @willwillis2381
    @willwillis2381 2 роки тому

    I got this unit and installed it in my 5th wheel trailer. Seems to work fine, ran my 1200w microwave for 30 seconds, did fine but noticed some squeeling. Seems ok but is that normal?

    • @LDSreliance
      @LDSreliance  2 роки тому

      Squealing? That doesn't sound normal. What about other appliances or devices? Do they behave normally?

    • @LDSreliance
      @LDSreliance  2 роки тому +1

      @Peter Hicks After thinking about it some more he may be referring to the warning sound when the inverter is getting low voltage. So you are probably right.

  • @mr.niceguy8960
    @mr.niceguy8960 4 роки тому +1

    Good afternoon sir, does it work if I used a 3000w inverter in 12v dv battery?? Thanks for your response😇

    • @LDSreliance
      @LDSreliance  4 роки тому

      I'm not sure what you are asking. Yes, you can use a 3000W inverter with a 12V battery.

    • @smoke_stackz3168
      @smoke_stackz3168 4 роки тому

      U need high ah rating battery not just 12v voltage

    • @dwightgumbs5073
      @dwightgumbs5073 3 роки тому +1

      You can run a much bigger one than that too. What is at question however is how long it'll run for.
      A 3000W inverter only burns ~3KW when it is outputting over 3KA at the outlet terminals.
      @90% efficiency a 3KW inverter will require a DC input of 3.3KW. At a constant 12V input, (this will vary), an input of 278A and that will require large cables and a VERY large battery if you want any reasonable time out of it.

  • @starchyoil
    @starchyoil 4 роки тому +1

    FYI, the coupon code doesn't seem to work.

    • @LDSreliance
      @LDSreliance  4 роки тому

      Try with the link: www.amazon.com/gp/mpc/ATQUDNCQ6JXGS and then the coupon code

    • @starchyoil
      @starchyoil 4 роки тому

      @@LDSreliance There's a notice on that link that says "Please return to this page to redeem discount after promotion starts on 05/11/2020 at 06:00AM PDT."

    • @LDSreliance
      @LDSreliance  4 роки тому

      Interesting. Sorry about that! I didn't create the code, the manufacturer did.

  • @paulmagee823
    @paulmagee823 4 роки тому

    Work great I’m running same inverter 👍👍👍

    • @LDSreliance
      @LDSreliance  4 роки тому

      How long have you been using it?

    • @paulmagee823
      @paulmagee823 4 роки тому

      LDSreliance over a year now no problems at all with it great inverter 👍👍👍

    • @LDSreliance
      @LDSreliance  4 роки тому

      Nice! Glad to hear it.

    • @paulmagee823
      @paulmagee823 4 роки тому

      LDSreliance do you do 24 volt version and how much in pounds please thinking ov upgrade???

    • @LDSreliance
      @LDSreliance  4 роки тому

      Yes they do have a 24v version. Not sure what that is in pounds. Here is a link to it on Amazon: amzn.to/2TbQhJk

  • @errolcain4071
    @errolcain4071 4 роки тому

    Hi good afternoon, Cai l get a 2000wt 12v to 220ac, please let me know

    • @jackpatteeuw9244
      @jackpatteeuw9244 4 роки тому

      Contact the company. It is a very minor change to get 220VAC output.

    • @errolcain4071
      @errolcain4071 4 роки тому

      @@jackpatteeuw9244 thanks very much for your reply

  • @theikhatua6599
    @theikhatua6599 3 роки тому

    Can an inverter power a home 24/7without going off

    • @LDSreliance
      @LDSreliance  3 роки тому

      Yes if you have enough battery capacity to keep up with demand.

    • @theikhatua6599
      @theikhatua6599 3 роки тому

      ok thanks very much

  • @Rampart.X
    @Rampart.X 2 роки тому

    I would have liked a test of the sine wave. Otherwise, cheers.

    • @LDSreliance
      @LDSreliance  2 роки тому +1

      I don't have an oscilloscope but I may add that to future videos if I can pick one up.

    • @Rampart.X
      @Rampart.X 2 роки тому

      @@LDSreliance - thanks. It's just that we wonder if some of these inverters REALLY produce pure sine waves.

    • @LDSreliance
      @LDSreliance  2 роки тому

      I agree 100%. I just haven't had hundreds of dollars laying around for a decent o-scope. These review videos don't make much ad revenue so it hasn't really been an option.

  • @davidjones1393
    @davidjones1393 4 роки тому

    THKS

    • @LDSreliance
      @LDSreliance  4 роки тому

      Thanks for watching, as always, David!

  • @Gebruikersstation
    @Gebruikersstation 3 роки тому

    is kevin spacy doing electricity classes now?

  • @wallacegrommet9343
    @wallacegrommet9343 4 роки тому

    Real output terminals

  • @bnwifi
    @bnwifi 4 роки тому +1

    ยี้ห้อนี้ทนมาก ผมใช้สูบน้ำมาหลายปี

  • @ramonbs6075
    @ramonbs6075 4 роки тому +4

    "reliable"... are they?

  • @williamsantiago320
    @williamsantiago320 4 роки тому

    Why do you use 4 batteries?

    • @LDSreliance
      @LDSreliance  4 роки тому

      Because none of them are strong enough by themselves to provide 3000W.

    • @ilingwang1168
      @ilingwang1168 3 роки тому

      @@LDSreliance Thanks for your video. Glad u updated the cables. The cables provided with the inverter are inadequate. I have the same inverter and ran mine with 2 x 1/0 cables on EACH terminal (equivalent to 4/0 per terminal) and I’m using 240ah lifepo4 batteries. I don’t have as much voltage sag with my lithium battery banks. I tested it without the terminal block and was able to pull 3000w with a hair dryer and a heat gun on the highest settings with no problem. I tested it with a clamp meter. I run most of my kitchen 24/7 with this system. Lesson, always OVERSIZE cables, especially for 12v. Your inverter will run more efficient, stay cooler and last longer. I personally, wouldn’t go any higher than a 3000w inverter on a 12v system. Thanks for sharing your experience.

  • @garrywhere7511
    @garrywhere7511 2 роки тому

    I wish if the government is going to stick their nose into our life. They would make sure that a product is as it says.

  • @GroundPoundersPlace
    @GroundPoundersPlace 3 роки тому

    nice not letting us see whether or not it handled the load

    • @LDSreliance
      @LDSreliance  3 роки тому +1

      Huh? I did show it handling the load.

  • @christoperun4380
    @christoperun4380 2 роки тому

    390 is affordable?

    • @LDSreliance
      @LDSreliance  2 роки тому

      Absolutely. Have you seen the price of many other 3000W models?

  • @renezepedarepreza7576
    @renezepedarepreza7576 4 роки тому

    corolla 13 can run 3000 watt inverter? r

  • @spike178
    @spike178 Рік тому

    $400 sounds a lot, what expensive $1000.

    • @LDSreliance
      @LDSreliance  Рік тому

      For a pure sine wave inverter that is pretty affordable.

  • @behemothinferno
    @behemothinferno 4 роки тому +3

    No output waveform testing? FAIL!

    • @LDSreliance
      @LDSreliance  4 роки тому +4

      Not everyone has an oscilloscope laying around. You can tell if it is modified sine wave from the buzzing of sensitive electronics, though.

  • @JohnSmith-ug5ci
    @JohnSmith-ug5ci 4 роки тому

    Buy American

    • @LDSreliance
      @LDSreliance  4 роки тому +1

      Please point me to any American company that manufacturers inverters in the United States.

    • @JohnSmith-ug5ci
      @JohnSmith-ug5ci 4 роки тому

      @@LDSreliancewww.toboaenergy.com/exeltech-inverters/
      energy.sourceguides.com/businesses/byGeo/US/byP/invert/byB/manufacturers/byN/byName.shtml

    • @LDSreliance
      @LDSreliance  4 роки тому +4

      John, I would love to be able to support those companies. But I am not wealthy. $863 for a 12V 1100W Pure Sine Wave inverter?? Good grief.

    • @JohnSmith-ug5ci
      @JohnSmith-ug5ci 4 роки тому

      @@LDSreliance Two things, one is you get what you pay for, china junk or American strong, and we have to decide if we want to sell out our country to commies or not.