Concept of Synchronizing Generators

Поділитися
Вставка
  • Опубліковано 4 жов 2024
  • This video explains how to synchronize two power sources. It discusses about various conditions required for synchronizing, practical implementation and various protections required.
    =========================================================================
    Links for Automation products:
    --------------------------------------------------
    1) Schneider Electric SR3B261BD Zelio Extendable Modular PLC
    amzn.to/3LNmdO9
    2) 3IDEA Snapmaker 3-in-1 3D Printer
    amzn.to/3SfSz6F
    3) Delta PLC, DVP28SV11R2, MPU with 16 DI; 12 DO
    amzn.to/3SnZvPu
    4) Delta ME Series VFD17AME43ANNAA 7.5Kw / 10 Hp Drive
    amzn.to/3CcJ4zL
    5) DELTA MS Series VFD VFD11AMS21ANSAA Single Phase 220V 2.2 KW
    amzn.to/3LPevn0
    6) Delta HMI & PLC USB Programming Cable UC-PRG020-12A DVP series
    amzn.to/3RhHj8K
    7) Compatible Siemens S7-200/300/400 PLC Programming Cable
    amzn.to/3dP7Ah2
    8) DIGIX-1-230V, DIGITAL I/O PLC
    amzn.to/3r6Etc5
    9) DELTA 2nd Generation DVP-SS2 Series Programmable Logic Controller
    amzn.to/3SjaYQ2
    10) CROUZET 88970051 PROGRAMMABLE LOGIC CONTROLLER
    amzn.to/3RfI9Tp

КОМЕНТАРІ • 35

  • @Goldies24
    @Goldies24 3 роки тому +3

    I applaud you as a good teacher. I am American and have difficulty understanding Hindi accents. Your narration here is very clear because 1) You enunciate each word 2) You speak at a slower pace. In EE speak - Your speech is critically damped and is frequency matched to allow for enough comprehension settling time. (I am an EE). Keep adding "the" before nouns - e.g. the generator, the load, the phase..

    • @starautomation
      @starautomation  3 роки тому

      I am an engineer.
      I had commissioned various synchronizing projects such as TG-TG, DG-DG and TG-DG along with power grid synchronizing projects.
      TG - Turbine Generator Set
      DG - Diesel Generator Set

    • @starautomation
      @starautomation  3 роки тому

      I am an engineer.
      I had commissioned various synchronizing projects such as TG-TG, DG-DG and TG-DG along with power grid synchronizing projects.
      TG - Turbine Generator Set
      DG - Diesel Generator Set

  • @rajeshmohan7881
    @rajeshmohan7881 Рік тому

    Very well explained with animations and graphs

  • @ZYXYZLF
    @ZYXYZLF 5 місяців тому +1

    Well explained 👏 Thanks for sharing knowledge ❤

  • @SPeeDKiLL45
    @SPeeDKiLL45 3 роки тому +1

    Thanks for the video bro very informative.

  • @dhadumia
    @dhadumia 4 роки тому +2

    Thank you to you brother!!

  • @bipulrawat3881
    @bipulrawat3881 3 роки тому

    Excellent video

  • @sugengriyadi414
    @sugengriyadi414 2 роки тому

    Very informative, but how about if the winding pitch generator is different.. For example 1 generator 0.66 pitch and 2 generator 0.86 pitch. What happen? And how the prevent the problem?
    Thank you Mr.

  • @marineengineerbudiriyanto.1969
    @marineengineerbudiriyanto.1969 4 роки тому

    Nice Explaination...brother

  • @johnsonponraj5286
    @johnsonponraj5286 Рік тому

    Can we synchronize 2 different MVA capacity Generators with existing main power Grid switchgear.
    We have a 6.6KV system and the plant load is 8MW. Present supply is taken from Government Grid through 33/6.9KV, 15MVA Transformer.
    The plant has excess gas, so plan to produce power through 2x1.5MVA, 6.6KV Generators and synchronize with 6.6KV Switchgear and consume the power internally.
    Is it possible to share the load as follows:
    Transformer - 6MVA
    Gen 1 - 1MVA
    Gen 2 - 1.2MVA

    • @starautomation
      @starautomation  Рік тому

      Yes. This is possible.
      Kindly share official enquiry in our email:
      satya.starautomation@gmail.com
      We will be sending our techno commercial offer

  • @Salah.alkhalifa
    @Salah.alkhalifa 4 роки тому

    If you have step up transformers after the 3 generators (that is 400v to 4160V)
    How do you take reference Voltage to feedback, at generator side of transformer primary or after the transformer secondary side? I believe it makes sense to take it at secondary via PT fed back to synch panel.
    What do you think?

  • @mohammedabdulsaleem3302
    @mohammedabdulsaleem3302 3 роки тому

    My dear is it possible to run all generators in parallel at different voltages?pl. Reply yes or no.

    • @billmoran3812
      @billmoran3812 3 роки тому

      When paralleled, the voltage at the generator terminals will all be the same as the bus voltage. However changing the voltage regulator settings will vary the excitation of each generator, causing the power factor of each generator to differ. With a difference of the power factor between generators a circulating current will result, flowing between the generators. This is detrimental to the operation of the paralleled system, because a portion of the generator excitation (voltage producing) capacity is wasted in circulating current that does not flow to the load and only produces heating in the generator windings.
      For this reason most modern voltage regulators are digitally controlled so that they control bus voltage equally.

    • @starautomation
      @starautomation  3 роки тому

      No.
      When DG is in synchronizing mode, voltage of all DG sets will remain same.
      During synchronized mode, when we control AVR then reactive power sharing between DG changes.

  • @masoudrahimi9148
    @masoudrahimi9148 5 років тому +1

    Hello sir I want sync 5 generator i need help me please

  • @fawzymuhammad8576
    @fawzymuhammad8576 3 роки тому

    Please sir how can I make syncrorism between two networks feed from different generation source?

    • @starautomation
      @starautomation  3 роки тому

      Kindly email me your project details do that we can suggest appropriate solution

  • @maureenngahu9867
    @maureenngahu9867 2 роки тому

    What synchronising controller were you using?

    • @starautomation
      @starautomation  2 роки тому

      In this project, we had used PLC control system for auto synchronizing and load management. However we had used a digital check sync relay also along with PLC logic.

  • @ahmedzarka3407
    @ahmedzarka3407 5 років тому

    Thanks ...

  • @newDestinations920
    @newDestinations920 5 років тому

    सर आपका training center कहाँ पर है?

  • @shojibhossain5677
    @shojibhossain5677 6 років тому

    sir inarter ac ar prametar ta jode akto dakaytan valo hoto

    • @starautomation
      @starautomation  6 років тому

      I cannot understand.
      Please write in English or in Hindi language