JSDesign_EngineeringTV
JSDesign_EngineeringTV
  • 169
  • 1 205 685
Practical Approach in Resolving Floor Vibrations
In this video, we will show you the most practical investigation of what and where are the causes
of typical floor vibrations that usually happen in concrete suspended slabs.
If you watch the whole video you will see the procedures and appropriate cheaper solution to resolve it.
Thanks
JSDesign Engineering
References:
NSCP 2015
ACI318-19
Переглядів: 259

Відео

Investigation and Upgrade of Exiting Foundation
Переглядів 57514 днів тому
This video is a best example of how to prepare a technical report of existing structure's present condition. In detail, it provide a good guideline starting from stability assessment to required upgrade or restoration. This guideline is also usefull as part of the structural calculation for building permit application. JSDesign Engineering Reference: NSCP 2015 ACI318-19
Analysis of Price Escalation on Concrete Supply
Переглядів 33928 днів тому
This topic is intended for cost estimators. Will give the viewers the correct tools and significant information guidelines on how to do it diligently. Please watch, learn and have fun! JSDesign Engineering
Design of Footing on BEDROCK
Переглядів 633Місяць тому
This video is rarely shown in a regular structural tutorials. It involves two (2) important concepts; first is why is it important to place footing below ground level, second is how to design a special attachment of foundation in case the underlying ground is happened to be a massive solid rock. Please watch the whole video to see how to treat them scientifically. JSDesign
How to Determine minimum concrete slab thickness (for 2-way slabs)
Переглядів 1,3 тис.2 місяці тому
In this video, you will see how code limits thickness of concrete suspended slab in structural design. Because preliminary size is important in design procedures, we should follow the proper way from the very start. Thanks for watching JSDesign Engineering Reference: ACI 381-19 NSCP 2015
How to Derive Productivity Rates in Construction
Переглядів 1,6 тис.2 місяці тому
This video is significant for construction estimators who wish to derive labor rates in much accurate way. It will show you guidelines on how to analyze labor rates of various activities by establishing parameters or actual site condition. Please watch and learn based from author's years of experience. JSDesign Engineering Reference: Collaborative contribution from site supervisors who has deca...
Connection Details, Metaldeck Flooring System to Concrete Beams or Walls
Переглядів 1,4 тис.2 місяці тому
This video will explain the importance of knowing how to detail metaldeck floor system, connected to Rc Walls or Beams. It will show 2 cases: (1) All new structures, (2) New metaldeck floor connected to existing beams or walls. At the end, complete rebar detailings will be presented for your quick reference. Note: these details are limited on residential liveload only. References: ASEP Steel Ma...
How to Prepare Recovery Plan on Delayed Projects
Переглядів 1,4 тис.3 місяці тому
This video contains tons of information and effective guidelines on how to prepare catch-up plan on delayed projects. The author highly recommends to complete the whole 20 minute video in order to have a full understanding about recovery measures. Have fun watching! JSDesign Engineering
Complete Foundation Design Guidelines
Переглядів 1,6 тис.3 місяці тому
This video is a complete summarized guidelines in preparing structural design of various foundation types. Please watch the entire 7 minute video and be educated on various foundation types and each applications. Thanks, JSDesign Engineering References: ACI 318-19 NSCP 2015
Series#3: Elevated Carpark, Design of Open-web Steel Joist
Переглядів 6713 місяці тому
This series#3, is all about design of the main horizontal support we call as Open-web Steel Joist. Utilizing those calculated forces from the previous series#2, you will see how "Principles of Stability" (short-cuts and technics) is being applied in order to analyze stresses of steel members including lateral loads. Please watch the 15-minute brief tutorial video and experience the proper way o...
Elevated Carpark Series#2 - Calculation of Earthquake Loads
Переглядів 1,3 тис.4 місяці тому
In this Series#2 of Elevated Carpark Design, you will see how Lateral Loads due to Earth movement are being calculated. Using provisions from NSCP 2015 such as base shear equation including all relevant coefficient for seismic known location and the soil type in the project site shall be applied in able to derive respective lateral loads per floor level. Have fun watching and learn in just 16 m...
Analysis and Design of 3-Level Carpark (Steel Framing)
Переглядів 1 тис.4 місяці тому
Analysis and Design of Elevated Parking Garage E.P. #1 Floor Layout and Preliminary load Assumptions. This video is part 1 of complete procedures of structural analysis, design of steel structures. It comes with useful tips and information on how to start structural design of a similar kind of structures. Please watch and learn the complete series to give you a free whole tutorials of design th...
Flat Slab with Drop Panel System
Переглядів 1,3 тис.4 місяці тому
Flat Slab with Drop Panel flooring is an innovative design of structural floor framing system. This video will guide you on how to convert the traditional beam-slab system into beamless design option. Please watch the whole video and see for your self which scheme is best in your proposed project. JSDesign Engineering
Foundation Structure on Sloping Ground
Переглядів 1,8 тис.5 місяців тому
In this video, you will learn how to determine the split elevation of structural foundations on sloping ground. The code specify a safe cut-slope requirement to in order to avoid possible erosion during construction and or during service. Please watch the entire 12 minute video to see how to do it the easy way. JSDesign Engineering
Beam Deflection
Переглядів 9296 місяців тому
Beam Deflection
How to Prepare Construction Work Methodology
Переглядів 1,9 тис.6 місяців тому
How to Prepare Construction Work Methodology
Structural Design of Concrete Zigzag Stairs
Переглядів 9366 місяців тому
Structural Design of Concrete Zigzag Stairs
What is Absent Loadings
Переглядів 6666 місяців тому
What is Absent Loadings
Reinforcing Bars Sizing for Cantilever Retaining Wall (Part 2)
Переглядів 1,1 тис.6 місяців тому
Reinforcing Bars Sizing for Cantilever Retaining Wall (Part 2)
Design and Analysis of Double Chamber Box Culvert
Переглядів 1,4 тис.7 місяців тому
Design and Analysis of Double Chamber Box Culvert
Design and Analysis of Concrete Retaining Wall
Переглядів 2,7 тис.7 місяців тому
Design and Analysis of Concrete Retaining Wall
Design of Steel Sheet Piles
Переглядів 1,5 тис.7 місяців тому
Design of Steel Sheet Piles
Estimate of Full Size Wooden Bedroom Cabinet
Переглядів 6347 місяців тому
Estimate of Full Size Wooden Bedroom Cabinet
Analysis and Design of Anchor Bolt on Railings
Переглядів 9128 місяців тому
Analysis and Design of Anchor Bolt on Railings
Theoretical Calculation of Masonry walls Compressive Strength
Переглядів 1 тис.8 місяців тому
Theoretical Calculation of Masonry walls Compressive Strength
Design and Analysis of Abovegrade Infinity Pool
Переглядів 1 тис.8 місяців тому
Design and Analysis of Abovegrade Infinity Pool
Design of Metal Deck System (Composite Floor Panel)
Переглядів 6 тис.8 місяців тому
Design of Metal Deck System (Composite Floor Panel)
How to prepare General Requirements in Construction
Переглядів 2,6 тис.9 місяців тому
How to prepare General Requirements in Construction
Design of Eccentric Footing
Переглядів 6 тис.9 місяців тому
Design of Eccentric Footing
Design and Analysis of Steel Purlins
Переглядів 4,8 тис.9 місяців тому
Design and Analysis of Steel Purlins

КОМЕНТАРІ

  • @cadassassins259
    @cadassassins259 11 годин тому

    napaka klaro. Salamat Engineer. new subscriber here from Saudi Arabia.

  • @geraldrabanal452
    @geraldrabanal452 День тому

    Sir ma clear ko lang po. Ung 4(5)/8(10) is equal po siya sa 25% po.

    • @geraldrabanal452
      @geraldrabanal452 День тому

      Nakalagay po is 20% may kinoconsider po ba dito sir?

    • @geraldrabanal452
      @geraldrabanal452 День тому

      If dlawa po ung c1 sir. Mag tatikes din po ba siya sa dalawa para makuha ung total weight times 20%

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 День тому

      @@geraldrabanal452 yes, that is correct

    • @geraldrabanal452
      @geraldrabanal452 День тому

      @@jsdesign_engineeringtv3633 pero sir. 25% po ba ito sir. Hehe medyo naguguluhan ako naging 20%

  • @manymul
    @manymul 2 дні тому

    Malaki yung span ng slab 4.3x4.5

  • @ajboi6480
    @ajboi6480 3 дні тому

    san po Sir yung correction ng (4+d) at (3+d) is s^2? thanks po

  • @jenajose1830
    @jenajose1830 3 дні тому

    Fresh grad civil engr po. Pwede kopo ba mhingi ung file neto?😅 Newly hired din po eh laking tulong po neto

  • @kenken5853
    @kenken5853 4 дні тому

    Engr.good morning po nagpagawa ako ng bahay bago palang po mga 10 mos.palang at yung wall ko at column nagkaroon ng vertical gap straight po hanggang taas ano po ba magandang gawin dun?at pano po naiiwasan yung ganun?nauna po kasi yung column ko bago po ako ng wall.Salamat po godbless

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 4 дні тому

      @@kenken5853 posible insufficient yung length ng dowels from column. Mag inquire ka sa concrete repair contractor kung pwede epoxy injection. Thanks

  • @PianoCharuzu
    @PianoCharuzu 4 дні тому

    analysis and design of pile foundation po engr. please

  • @UwU_UwU_69
    @UwU_UwU_69 6 днів тому

    Allowed po bang gumamit ng 12mm rebars for beams on two storey residential building? Thank you po.

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 6 днів тому

      @@UwU_UwU_69 minimum 16mm main bars, baka hindi ma approve sa building permit if you use 12. Thanks

    • @UwU_UwU_69
      @UwU_UwU_69 6 днів тому

      @@jsdesign_engineeringtv3633 salamat po sir. Nag fail po kasi pag 16mm Ang ginagamit sa design pero pass naman po pag 12mm ang ginamit. Di ko lang mahanap sa NSCP kung may section na nag sasabi na prohibited to use 12mm rebars for beams and column. Maraming salamat po sir. Godbless po.

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 6 днів тому

      @UwU_UwU_69 try to increase numbers of rebars in critical section but make sure to check clear space between bars, or increase beam depth. Thanks

  • @melchizedekpeneba607
    @melchizedekpeneba607 6 днів тому

    Good day po Engr, pede po ba makahingi ng reference kung bakit po structural slab ang design pag Heavy storage facilities, need ko lang po sa thesis ko po, salamat po

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 4 дні тому

      @@melchizedekpeneba607 It's a designer's discretion. Not always structural slab. You can use slab-on -grade if subgrade and subbase are reliable. Thanks

  • @eldefredocarillo4279
    @eldefredocarillo4279 8 днів тому

    Sir, send me your tabulation and design & computation regarding 2story house. Size of footing, column & beam and rebars. Thank you po!

  • @harleyjunecelicious1206
    @harleyjunecelicious1206 8 днів тому

    Engr. Tanong ko lang po anong approach po Ang pag compute sa 2nd floor na slab kung naka tubular lang tapos Marine plywood Ang nag sisilbing flooring niya

  • @DRCE777
    @DRCE777 9 днів тому

    THank you engr, love your videos po. practical real world problem approach 😊😊

  • @oslekcom1
    @oslekcom1 10 днів тому

    in my experience, static base shear is calculated from the tower down on top of the grade. in this case tower plus podium without parking since they are below the grade. run your response analysis then calibrate it to your calculated base shear. then check drift and design the lateral resisting elements.

  • @hopebrazil1545
    @hopebrazil1545 10 днів тому

    Sir, ano pong code yung Coefficient method?

  • @rufino-s4y
    @rufino-s4y 11 днів тому

    Sir yong addl bars sa bottom ay naka weld ba sa steel deck or spot weld lang

  • @nestornavarro6548
    @nestornavarro6548 13 днів тому

    Hello 👋👋👋 sir gd day, po. Sir request lang sana ako kung pede po ba kayo mg vlog topic sa pag design ng slope of roofing with regards to wind loads, e.g. anong slope ng roofing ang gagamitin kapag my given na wind velocity o wind load. Ano po ang mga parameters sa pag design ng solpe of roofing na i consider yong wind? Sana po sir mapa unlakan nyo po ako, maraming salamat po. Have a nice and a blessed day, po sir.

  • @jonjiekhyzzer8404
    @jonjiekhyzzer8404 13 днів тому

    Thank you sir.

  • @Ralphdennis417
    @Ralphdennis417 13 днів тому

    Sa compression daw maganda, pero posible nmn na wala xD

  • @justinebautista9926
    @justinebautista9926 15 днів тому

    Salamat sa video tutorial engineer. Pwede ko po ba ako makahingi ng copy ng excel file. thank you

  • @Ericaldreen
    @Ericaldreen 15 днів тому

    napaka underrated ng channel sobrang informative

  • @AxlJonDelRosario
    @AxlJonDelRosario 16 днів тому

    hello sir thank you for this video. but can I ask if the safety factors is computed or constant? if that is constant where can i find that reference.

  • @setbabista6108
    @setbabista6108 16 днів тому

    Sir my question po sana ako pno po ako makaka personal mssge sa inyo

    • @setbabista6108
      @setbabista6108 16 днів тому

      Sir hingi Sana ako tulong and advice regarding sa vibration NG slab ko po ng garage nasundan ko po yung blog nyo ang problema Lang po my biga po yung saakin sa gitna ano pong magandang gawin Doon pano ko po kyo MA PM

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 16 днів тому

      @@setbabista6108 please send message to JSDesign fb. Thanks

    • @setbabista6108
      @setbabista6108 8 днів тому

      ​@@jsdesign_engineeringtv3633 hello po sir diko po makita exact page nyo e gusto ko sanang mag mssge po e

    • @setbabista6108
      @setbabista6108 8 днів тому

      Baka po pwedeng sa send NG link

  • @alladinebrahim7983
    @alladinebrahim7983 16 днів тому

    Hi engr., hindi na po ba magmamatter kung kahit anong size ng beam ang iaassume natin sa calculation ng DEAD LOADS?

  • @cadworkz
    @cadworkz 16 днів тому

    Thank you po ^^

  • @wilsonbrua8691
    @wilsonbrua8691 17 днів тому

    Ako din layman term

  • @maicosaguin8397
    @maicosaguin8397 19 днів тому

    need ba mag ductile design sa 3 storey residential house at 2 storey apartment bldg? thanks po sir

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 18 днів тому

      @@maicosaguin8397It depends, If lateral load prevails against DL & LL you have to consider ductile design. Thanks

  • @joselitocancino1922
    @joselitocancino1922 22 дні тому

    Engr tanung lng po ung ginwa k po doon s metal deck k hnd po monolithic ok lng po b un?3rd floor with roof top po ung hnd monolithic nauna po ung beam bago po ung metal dec po..ayos lng po b un?

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 22 дні тому

      @@joselitocancino1922 posible naman yan, I have a video that shows how to connect metaldeck to existing beam. Browse mo channel ko. Thanks

  • @allaboutanythings
    @allaboutanythings 23 дні тому

    hello Sir clarification lang po regarding your formula for Po, paano nyo po na derive yung Po = 2092 Kn from Po= 0.85 (21) (00186) + (400) (4x201) medyo nalito lang po ako iba kasi nakukuha kong result. thanks for your reply in advanced.

  • @norjannahlanto7099
    @norjannahlanto7099 25 днів тому

    Hello, sir. new fan po. pwede malaman ang name ng book?

  • @WilbertDiwan
    @WilbertDiwan 26 днів тому

    Thanks po sa video Sir, copy nga po ng templates nyo,, thanks verry much po

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 26 днів тому

      @@WilbertDiwan please send your message to JSDegn fb. Thanks for watching

    • @WilbertDiwan
      @WilbertDiwan 26 днів тому

      @jsdesign_engineeringtv3633 a ok po thanks a lot po,,, God Bless

  • @WilbertDiwan
    @WilbertDiwan 26 днів тому

    Good day po thanks verry much sa videos nyo verry helpfull, pwede po ba maka avail sa program nyo?

  • @ajiriltomas9026
    @ajiriltomas9026 26 днів тому

    Im licensed engineer last 2017, pero nagrefresh ako dis 2024.hehe narecall ko naman lahat sa explaination mo sir. Malinaw

  • @ajiriltomas9026
    @ajiriltomas9026 26 днів тому

    Thank you sir

  • @litosy6751
    @litosy6751 26 днів тому

    sound test

  • @NonilonLim
    @NonilonLim 29 днів тому

    Gud am sir,Yong poste at beam kailangan po ba e add on SA weight of concrete?

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 29 днів тому

      @@NonilonLim No. As explained in the video, the factor that we use is for complete system. Thanks for watching and comment!

  • @pobrengengineerd9797
    @pobrengengineerd9797 29 днів тому

    Thankyou sir always😊

  • @user-vz6uk2ke8h
    @user-vz6uk2ke8h 29 днів тому

    hello! baka po meron sainyong may moment coefficient table pls

  • @febryugalde4671
    @febryugalde4671 Місяць тому

    Sir Subscriber nyo po Pwede pashare po ng templates sir para mapag aralan ko po sir.. Maraming Salamat po sa mg Videos sir, Maraming Learnings po..

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 Місяць тому

      @@febryugalde4671 please send message to JSDesign fb. Thanks for watching and comment

  • @jekiro020
    @jekiro020 Місяць тому

    Thank you Engineer sa mga videos mo. Ngayon ko lang nadiscover ang channel mo sobrang laking tulong ng mga uploads mo sa isang tulad kong nagsisimula pa lang na Civil Engineer.

  • @jekiro020
    @jekiro020 Місяць тому

    Engr tanong ko lang po pag ganitong approach puro self weight lang po ng concrete hindi na po nasasama ang live loads?

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 Місяць тому

      @@jekiro020 yes that is correct. But the factor that I used considers complete system (finished structural shell), meaning that includes liveload already. It's a good start to determine preliminary footing size. Thanks

  • @ASDSADD-h5j
    @ASDSADD-h5j Місяць тому

    Good day sir and everyone... Bagong graduate lang po ako from university BSCE, meron po ba kayong advice na channel like this or topics, resources na pede kong aralin to practice designing po. Gusto ko po sana iself study muna before taking masteral kung sakali. Thank you sa sasagot I will appreciate it. Godbless.

  • @reymondbajado8877
    @reymondbajado8877 Місяць тому

    sa po ba talaga sir ung tamang splicing zone ng column ? ung sa iba kasi nasa mid-height or L/2 thank you

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 Місяць тому

      @@reymondbajado8877 In general that is correct. But strictly speaking, stress diagram will show the right location. Thanks for watching and comment!

  • @jennaprincipe4013
    @jennaprincipe4013 Місяць тому

    thanks sir and more power :)

  • @johny9083
    @johny9083 Місяць тому

    Sir ask ko lang sa design ba ng wedge anchor bolt same lang sa explanation sa video ? I mean yung minimum bolt pretension(230kn) is also same sa pull out force in tension ng wedge anchor bolt? If ever na yung pull out force ang gagamitin, same din lang ng calculation sir ? Sana po masagot

    • @jsdesign_engineeringtv3633
      @jsdesign_engineeringtv3633 Місяць тому

      @@johny9083 No, you cannot use formula provided by code on regular anchor bolt to wedge anchor bolt. These are specialty products, I suggest to look for manufacturer's catalogue for various sizes and corresponding pull-out stregth. What I know, there is a required tightening or torquing to reach its desired expansion to develop better grip. I hope that answers your question. Thanks for watching and comment!

    • @johny9083
      @johny9083 Місяць тому

      @@jsdesign_engineeringtv3633 salamat sa pag reply sir

  • @Bossj312
    @Bossj312 Місяць тому

    Engr.mas madali kong maintindihan kapag actual tutorial sana may actual kang video po.

  • @salvadorbenitez6770
    @salvadorbenitez6770 Місяць тому

    Thank u ..

  • @leijitauro588
    @leijitauro588 Місяць тому

    Sir may sample computation po for road slab naman po? considering moving vehicles

  • @optimusg9391
    @optimusg9391 Місяць тому

    Di ang daming bakal niyan.

  • @aarongolimlim3060
    @aarongolimlim3060 Місяць тому

    hello po, sir san po nakuha na libro yung cross section

  • @maicosaguin8397
    @maicosaguin8397 Місяць тому

    thanks po